Discussion in 'Electrics UK' started by Josh Miller, 30 Dec 2019.

  1. Josh Miller

    Josh Miller

    Joined:
    30 Dec 2019
    Messages:
    16
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,

    I fitted a new shower back in July, went for the exact same kW and everything has been great until this week when I stopped getting 240V at the shower.

    All I can find is the breaker but there doesn't seem to be an isolation switch anywhere or a fuse, I don't have any power at the shower checked across the supply and earth and its 0V, so I went to the MCB and the breaker hasn't tripped, checked on supply to the breaker and its giving 240V, checked the other side and its sending 240V out, turn the breaker off and it's 0V as it should be.

    I'm scratching my head and thinking I may have a break in the wire or there's gonna be a fuse or isolation switch somewhere but I can't find either anywhere, could it be the earth in the MCU Unit is a poor connection?

    If I check the breaker and use the showers earth cable in the MCU and not on the earth bar in the MCU would that rule out the showers earth cable?

    Thanks in advance.
     
  2. Sponsored Links
  3. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    63,706
    Thanks Received:
    3,369
    Location:
    Gosport
    Country:
    Cook Islands
    It's usually a wire burned out at a poor connection in the switch.

    It's strange not to have a switch. If not a pull cord on the bathroom ceiling it may be a wall switch (should be lot chunkier than a light switch or socket switch)

    Or there might be a junction box hidden in the ceiling.

    Might be a connection inside the shower.
     
  4. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,353
    Thanks Received:
    896
    Location:
    Dorset
    Country:
    United Kingdom
    He says there isn't an isolator, though in practice there nearly always is one somewhere.

    Have a good luck for the switch, it may be in some weird place which made it easy for the installer, it may even be chucked under the floorboards/slung in the loft if your place has 'history'.
     
  5. HERTS P&D

    HERTS P&D

    Joined:
    9 Apr 2010
    Messages:
    10,041
    Thanks Received:
    1,489
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Have a look in the air-in cupboard, maybe it has been knocked to the off position.

    Andy
     
    • Like Like x 1
  6. Josh Miller

    Josh Miller

    Joined:
    30 Dec 2019
    Messages:
    16
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,

    Thanks for the replies already, I didn't think of checking in the loft so I'll have a look up there, I'm just on with removing all the silicone sealant around the bath hoping there's one under there for some strange reason.

    No airing cupboard in the house but good shout.
     
  7. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,353
    Thanks Received:
    896
    Location:
    Dorset
    Country:
    United Kingdom
    Such fun.
     
  8. Josh Miller

    Josh Miller

    Joined:
    30 Dec 2019
    Messages:
    16
    Thanks Received:
    0
    Country:
    United Kingdom
    Well I'm underneath the bath, there's no switch or fuse but the earth, neutral and feed seem to be connected here, the earth and feed have insulation tape wrapped around and the neutral is connected with a scotch lock.

    I'm from the motor trade and we rarely see jobs this bad anymore, looks like a mate has done this rather than a professional but it could be the norm for all I know but I'm gonna have to test either side of the connection to see if this is my fault but the access is crap!
     
  9. HERTS P&D

    HERTS P&D

    Joined:
    9 Apr 2010
    Messages:
    10,041
    Thanks Received:
    1,489
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Post some pictures.

    Andy
     
  10. Sponsored Links
  11. Josh Miller

    Josh Miller

    Joined:
    30 Dec 2019
    Messages:
    16
    Thanks Received:
    0
    Country:
    United Kingdom
    So I've pinned into either side of where it looks like they're connected and I'm not getting any readings, I've been in the loft and can't see an isolation switch, there's no pull cord isolation switch but everything checked out in the MBU as I've literally just triple checked, switched off all the power and removed the earth and neutral just to check their connections.

    Maybe the earth connection is fine as I've checked in the MBU just on the showers earth with the breaker feed and I'm getting a reading, so if I check either side of the supply where its joined underneath the bath that should tell me if the connection is fine but how do I check that with the multimeter?
     

    Attached Files:

    Last edited: 30 Dec 2019
  12. Josh Miller

    Josh Miller

    Joined:
    30 Dec 2019
    Messages:
    16
    Thanks Received:
    0
    Country:
    United Kingdom
    We have this switch but it's only got a 5amp fuse in and I've swapped it.

    Does anyone know what it is? It's in our main bedroom.
     

    Attached Files:

  13. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    3,850
    Thanks Received:
    775
    Country:
    United Kingdom
    Its a switched ,fused ,connection unit. Does it feed an outside light ,possibly ?

    Certainly not something you would have on an instantaneous electric shower circuit.
     
  14. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    3,850
    Thanks Received:
    775
    Country:
    United Kingdom
    You should remake the connections in a suitable junction box ,what you have is a right bodge.
    What are you using to test that the line conductor is live ?
    Multimeter ? Measure voltage Line to neutral ,and line to earth ?
     
    Last edited: 30 Dec 2019
  15. Josh Miller

    Josh Miller

    Joined:
    30 Dec 2019
    Messages:
    16
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi Terryplumb,

    I agree it's a mess, I'll pick one up from screwfix anything I need to look out for or just any 3 way junction box? I'm using a multimeter just checking voltage across the power and earth line, I've left the neutral out as I should have a reading across those two.
     
  16. Josh Miller

    Josh Miller

    Joined:
    30 Dec 2019
    Messages:
    16
    Thanks Received:
    0
    Country:
    United Kingdom
    Must be for an old outside light I guess, doesn't seem to switch anything off in the house.
     
  17. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    3,850
    Thanks Received:
    775
    Country:
    United Kingdom
    Have you taken voltage readings on the cables under the bath ?