Economy 7
Status
Not open for further replies.
Re posting so the op does'nt lose the answers he needs in this sea of drivel from bas and softus.
holmslaw";p="973728 said:
A relative has just had this removed and central heating put in. Can the power point fronts be changed for 13A sockets instead?
You must ensure that disconnection time of 0.4 secs can be achieved, otherwise no problem, you will need a spark to check the disconnection times.
The regs and part p are not retroactive for that reason you do not have to install an RCD - although it might be a good idea to do so.
Bas/ softus I think you should read part P, as you are obviously unaware of the details, you can see it here.
http://www.planningportal.gov.uk/uploads/br/BR_PDF_ADP_2006.pdf[/QUOTE]
No - what I can see there, and what you've failed to see properly because it appears you're not too good at reading is Approved Document P, not the actual law.
You will note that it only applies to domestic installations, and certain works are exempt eg replacing socket outlets.
No - what I will note, and what you have failed to note because it appears you're not too good at reading is that some work is exempt from NOTIFICATION, which is not the same at all as not being required to comply with the rest of the provisions in The Building Regulations.
Sofus said "So in one breath you are claiming that you don't have to comply with something which is mandated by law" - I never said that!
It was I that wrote that, not Softus, but then you probably didn't spot that because you're not too good at reading.
What I said was ",You do NOT have to comply with Part P because you are only replacing some spurs with sockets."
I know that's what you said.
And you are wrong - you do have to comply with it, it being the law.
Sofus said "and in the next you're claiming that it's garbage to say that you don't have to comply with something not mandated by law."
- I never said that either.
You do NOT have to comply with The 17th edition because the regulations are not retroactive.
For domestic work, nobody has to comply with the 17th Edition.
An often stated piece of garbage
You seeem to be getting a little confused. :lol: :lol: :lol:
I think not...
Well - I'm sorry you regard it as drivel to point out what the law says.
Anyway - I'm going out, maybe somebody else can try and make you understand that whilst contravening Part P might not have serious consequences it is irresponsible of you to tell the OP that the law doesn't actually apply to him.
I never said the law did'nt apply to him. I said it does not apply to replacing some spurs with socket outlets.
But that is what he is doing.
And the law makes certain requirements in respect of that work.
So it does apply to him.
P1 of Part P: "P1 Reasonable provision shall be made in the design and installation of electrical installations in order to protect persons operating, maintaining or altering the installations from fire or injury. "
This applies to all work on LV and ELV systems in domestic dwellings in England and Wales.
Schedule 2B details what work is non-notifiable, even if it is non-notifiable the work still needs to comply with P1.
Non-notifiable, means Mr Joe Bloggs you don't have to tell anyone that you are changing some spurs to socket outlets.
Yep, but at the same time you must ensure what you are doing complies with P1 i.e. it has to be safe.
I agree with your thoughts, but the point is part p doesn't say he has to have it tested, just replace like for like (almost) job done. The job is so simple that is extremely unlikely to make the installation unsafe(r) - and I know their are people who could screw it up - but thats beside the point.
If you replaced a s/o or a switch in your home and did'nt have any way of testing it was safe would you be bothered - I don't think so.
So if you replaced all your hard wired FCUs with socket outlets, what provision for RCD protection have you got? Without RCD protection, do the circuits comply with P1 i.e. has reasonable provision to protect persons operating the installation from injury been made?
And (this is a genuine Q - I've not got any books with me), if the heaters were on BS3036s is there an absolute guarantee that disconnection times will be low enough for handheld appliances?
There's a good chance they'll be fine:
Maximum Zs for 0.4s disconnection times.
15A - 2.55ohms
20A - 1.77ohms
Even when reducing the figures to 80% to compare them to measured or calculated EFLI values there should still be enough headroom for a 2.5/1.5 radial.
Well this is where you need an electrician to do the work properly. A diyer is not going to be able to figure out whether a 0.4 second disconnection is acheivable unless he/she is skilled in electrical work. We still don't know whether the OP is using a sparks or aiming to do the work themselves. A 15A BS3036 will require a max of 2.67 Ohm Zs, which is probably acheivable, but then there's the question of upgrading to RCD protection to comply with 2008.