Discussion in 'Electrics UK' started by Sid1968, 28 Aug 2021.

  1. Sid1968

    Sid1968

    Joined:
    12 May 2016
    Messages:
    148
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi need some advise please
    Attended property to re wire 5 flats.
    The flats has electric only single phase 100amp fuse.

    Now the owner wants in each flats 5 of each
    8.5kw shower x 5
    5.5kw water heater x 5
    2 kw wall heaters x 10 plus
    3 kw hob x 5

    Thats over 100kw from each flat an thats not taking power and lighting circuit into account.
    That equates to well over 400kw from a 100amp fuse??

    Oh not to mention all flats will be submetered.

    Will a 3phase supply application suffice?
     
  2. Sponsored Links
  3. Guitarguy

    Guitarguy

    Joined:
    26 Mar 2009
    Messages:
    255
    Thanks Received:
    18
    Location:
    Wiltshire
    Country:
    United Kingdom
    I’d say a 7 way ryfield distribution unit supplied by 95mm cable would be what’s needed, a standard 3 phase supply would struggle, you’d have to share two of the phases not to mention overloading the neutral conductor
     
    • Like Like x 1
  4. aptsys

    aptsys

    Joined:
    16 Sep 2007
    Messages:
    1,869
    Thanks Received:
    151
    Country:
    United Kingdom
    You may need a separate supply for each flat, or suggest other forms of heating, but you don't just add up the rating of every appliance to work out the supply requirements.
     
  5. Sid1968

    Sid1968

    Joined:
    12 May 2016
    Messages:
    148
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi aptsys
    For future reference how to do u calculate the max load?
     
  6. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,914
    Thanks Received:
    1,985
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Double insanity.

    6x new supplies required.
    5 flats plus one for the common parts.

    If they want to reduce costs, say goodbye to instant electric showers and instant water heaters.
    One hot water cylinder per flat will reduce the total load significantly.
    However still needs individual new supplies for each flat.
     
    • Like Like x 1
  7. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    4,531
    Thanks Received:
    942
    Location:
    Durham
    Country:
    United Kingdom
    Landlord is being a shoddy so & so. If there's gas to the house he'd be far better off putting a gas boiler & a good sized cylinder in & using hot water meters to each flat. Cost for 5 new supplies could be very high....
     
  8. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,914
    Thanks Received:
    1,985
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    It certainly will be.
    Landlord either pays for it, or sells the place if they really can't afford it.

    Regardless of the heating or fuel arrangements, 5 individual flats requires 5 individual supplies.
     
  9. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    74,219
    Thanks Received:
    4,284
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    Apart from the landlord being barmy, he is assuming that he can find good-quality tenants willing to pay four or five times as much for energy, as they would if they lived in a home with gas heating.

    Good tenants will be looking for a better home no later than the day the first winter bill comes in.
     
  10. Sponsored Links
  11. AdrianUK

    AdrianUK

    Joined:
    22 Sep 2009
    Messages:
    609
    Thanks Received:
    91
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Care you explain how you think that's possible?
     
  12. wundaboy

    wundaboy

    Joined:
    27 Apr 2008
    Messages:
    135
    Thanks Received:
    16
    Location:
    Shropshire
    Country:
    United Kingdom
    Not doubting you but I find this hard to believe, could you clarify?
    Is all this entirely correct? 5no 3kW hobs in one flat??

    1) What exactly is the size of the current incomer

    2) What is the total load (leaving aside diversity) per individual flat?

    3) What would be the total building load (leaving aside diversity)?

    If this is accurate, it sounds like each flat would need its own 100 amp 3 phase supply, and even then with diversity it would barely be sufficient. Sounds terrible!
     
    Last edited: 30 Aug 2021
  13. Sid1968

    Sid1968

    Joined:
    12 May 2016
    Messages:
    148
    Thanks Received:
    0
    Country:
    United Kingdom
    Orginal post it states 5 flats off one 100amp supply so all appliances x 5
     
  14. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,178
    Thanks Received:
    553
    Location:
    London
    Country:
    United Kingdom
    No it doesn’t. It states 5 flats with 5 of each item in each, that’s 25 of each item. Badly written but that is what it says.
     
  15. Sid1968

    Sid1968

    Joined:
    12 May 2016
    Messages:
    148
    Thanks Received:
    0
    Country:
    United Kingdom
    D
    Sorry yes yur correct incorrect info

    Tot 5 flats each appliances in each flat
     
  16. wundaboy

    wundaboy

    Joined:
    27 Apr 2008
    Messages:
    135
    Thanks Received:
    16
    Location:
    Shropshire
    Country:
    United Kingdom
    Reading between the lines I'd guess the owner won't want to pay to have this done properly, i.e. supply upgrade. I'd walk away from it.
     