15YO boiler condemned as flue too long??? Please advise?

Joined
4 Jun 2007
Messages
38
Reaction score
0
Location
London
Country
United Kingdom
Hello,
After fixing my Glowworm Swiftflow 75E I decided to get some insurance including a service and safety check.
So I did some investigation on the Internet and went for a deal with my current provider’s policy.

During the service I briefly spoke to the engineer on the phone, who said the flue is too long and there's no terminal. I then had to go to a meeting so didn't speak again. The engineer explained nothing to my wife who was home at the time.
When I got home there was a big red danger sticker on the boiler and a gas installation warning notice. Also, the service check list has not been completed apart from additional information regarding the flue length.

The maximum flue length in the installation manual (which I left available for the engineer) is 2833mm; my measurement of the flue, being VERY generous on both the wall thicknesses is 2740mm. The boiler is in a cupboard next to the bathroom and extends straight through the bathroom and outside wall (no bends).

The boiler has been installed in the house for the 11 years I have been there, and probably another 4 judging from the model.
Is the Engineer correct? I accept there's no terminal guard, which is easy to remedy.

Thanks
 
Sponsored Links
Sponsored Links
No bends it is a straight side flue as below.

6977127459_4fc74fa6f0_z.jpg


6830999866_9051d99377_b.jpg


6831000022_c84c808b95_z.jpg


Cheers
 
On the face of it the engineer was wrong and ask the company to clarify. If you have no joy there then complain to Gas Safe.
 
Many thanks, I wanted some advice before contacting the company.

Also, on the service record the 30 point check list hasn't been filled out.
Could this indicate he didn't do a service.??

Cheers
 
Hi, I checked the flue terminal this morning and found that it had fallen behind the garden shed. I have now re-attached:


6833415986_db4384484b_b.jpg

6833416168_2a7e83e763_b.jpg


I'll also order and install a terminal guard and repair the rendering around the flue.

With the terminal problem sorted, should I go back to the company and ask for a second opinion about the flue length?
I quite sure it's within the installation manual guide lines.

Many thanks.
 
It fits snuggly around the inner exaust pipe.
I also added a very thin layer of silicone, but was going to do some research on the heat/steam tolerance.

I think originally it was held in place by concrete. The entire installation looks a bit cowboyish to me. It happend when the property was council owned.

Is what I've done dangerous?

Thanks
 
Silicon is not a suitable material to hold a flue outlet together.
nor is a flue terminal held together by concrete
 
In the time it took that Engineer to do all that paperwork (AR) he could have found the terminal, fixed it back with a couple of self tappers, measured the flue length to compare with MI's - if that terminal is less than 2 mtr from the ground it will need a wire guard this could be classified as NCS at worst, but then some companies see a boiler of that age and think pound notes!!£££££££££££££££££££££££££ :(
 