You wouldn't have RCD's before other RCD's if designed correctly.
Agreed not two 30 ma ones
If the new regs want all these rcd's then
With a TT supply how would you avoid having a 30 ma after the 100ma one
You wouldn't have RCD's before other RCD's if designed correctly.
Same way you do now - a board with separate sections, not the conventional split-load design which is really only suitable if the incomer is just a switch...If the new regs want all these rcd's then
With a TT supply how would you avoid having a 30 ma after the 100ma one
Not only unreasonable, but pointless in an RCBO, because the neutral current and the phase current had better be within 30mA of each other - you can't overload just one...It is not very common, and I connot think of any reasonable reason why you would want to use a true Double Pole to monitor the neutral in a single phase situation.
Hmm - well ignoring the mixup of "phase", "live" & "neutral" terms (A Single Pole Switched Neutral simple switches the phase at the same time as the live, but only the live pole will operate due to overcurrent.
You wouldn't have RCD's before other RCD's if designed correctly.
Agreed not two 30 ma ones
If the new regs want all these rcd's then
With a TT supply how would you avoid having a 30 ma after the 100ma one
house in the country with TT supply
the "main" RCD is 100mA with a 100mSecond delay, so it will not trip if there is another RCD protecting the faulty socket circuit (because that one will usually be 30mA, and is not time-delayed, so the fault will be cleared before the delay expires)
however, it would trip if here was a fault on a circuit which did not have a non-delayed RCD on it
You remove the 100mA from the supply, and put it into the CU.With a house in the country with a 100 ma trip on the supply,How can you design that correctly and not have an rcd before another rcd.
ie 100ma before a 30 ma
Thanks
Yup - something like that.something like this?
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local