3 Phase?
10 Jul 2006
Cleveland
TT System, 2 overhead lines, 3 incoming fuses providing 3phase supply. How is this with only 2 overhead cables?
Are you sure it is a TP supply?
Could it just be three single phase supplies?
This is a 3no. SP supplies, yet it uses a TP head and meter
The only way to know for sure is to test the voltage between phases.
If it is a TP supply then you will typically get a reading of between 400V & 440V (U) and between 230V & 250V (Uo)
Don't know why three SP supplies? Maybe a single 100A supply was not big enough, and the cost of upgrading the DNO transformer and wiring prohibited the installation of a TP supply?
That would be my guess. Are you sure there isn't another supply coming into the property from somewhere else?
Short of having a big transformer / invertor somewhere you can only have a single phase supply on two wires.
I don't think it is personally. The DNO neutral appears to be 16.0mm² with potential to be carrying 300A :shock:
If there are only 2 wires then it can only really be a single phase supply. Wether or not the 2 wires are phase and neutral depends on the DNO setup, they may be 2 phases if they are feeding a transformer.
I must admit, I didn't like the look of RFs cutout the first time I saw it either.