3 port valve problems

Joined
6 Sep 2008
Messages
2
Reaction score
0
Location
Birmingham
Country
United Kingdom
hello ... i seem to be having problems with the three port valve on my central heating system its a honeywell i changed the head motor today because it wasn't switching to ch but still no joy they dont seem to be any power to the motor . but i dont know where the power comes from timer / room stat ect . the timer i have is a acl switchmaster sm400 .manualy moving the lever to ch works ok but with the motor out of the head the cog dont move .
 
Sponsored Links
Have you got 240v power on the grey/cylinder stat and or 240v on the white/room stat
 
the five wires from the valve head.tested at the numbered distribution board
blue wire 0v
orange wire 240v
white wire 240v
grey wire 0v
 