30 amp /32 amp breaker ?

Joined
18 Oct 2012
Messages
1
Reaction score
0
Location
Birmingham
Country
United Kingdom
just got a new electric cooker states in the installation guide must be connected to a 32 amp supply, existing is 30 amp, any advice on the outcome of using off the existing breaker and or any advice on changing the breaker to 32 amp, cheers folks !!!!!!!!!!!!!!!!!!!!!!!!!!
 
Sponsored Links
In the main MCB's go 6, 10, 16, 20, 25, 32, etc and a fuse 5, 10, 30, etc. So when a light fitting is rated 5A supplying with a 6A MCB is OK and other way around when a 32A supply is requested from an MCB using a 30A fuse is OK.

There are one or two exceptions to the rule semiconductors often have to use fuses not MCB's as an MCB is too slow but normally one thinks of 30A and 32A as being the same.
 
In the main MCB's go 6, 10, 16, 20, 25, 32, etc and a fuse 5, 10, 30, etc.

True, although earlier MCBs, eg. original MK Sentry range, Crabtree C50 range and others did come in 15A & 30A sizes...

...but that's just me being difficult!

Yes, for practical purposes 30/32A can usually be regarded as the same.
 