Range cooker at 15.6kw..spec sheet requirea cooker box at 67.8 amps..is there such a thing.looked on Mk and can find 45amp
any body shed some light?

Cheers
 
Got the spec sheet yes a big mother f**ker
will 10mm cable suffice as well as this 67amp switch????
 
You dont need a 67 amp switch. Use 10mm² with a 50A MCB and 50A cooker switch (if these exist, i know 50A pullswitches exist)

To acheive a 67A rating, you'd need the next size up from 63A, which is 80A. However, with such a huge appliance, its unlikely that all the elements will be burning at once. :wink:

Are you doing this in your own home? Do you know about part p?
 
To supply 68A you will need either a 16.0mm² t&e or maybe even a 25mm² supply depending on how it is run in.

Is this an industrial cooker, as I have never seen a domestic cooker requiring such a large supply.

The largest rated standard switches are 50A, so anything above this will require an industrial switch.
 
I am moving theorigianl oak lintel to a higher position in the chimney breast to allow the cooker to go into the opening,but i need to run cables as there will be no access for the cooker fitters,was just interested as to the high rating of the switch
 
RF Lighting said:
The largest rated standard switches are 50A, so anything above this will require an industrial switch.
or a CU style switch in a modular box.
 
Not very domestic... except that a commercial kitchen would have gas burners not a ceramic hob.