I have the opportunity of installing the wiring for shower, extractor, isolator and fused spur for elv waste pump in 60 flats ( retirement home). I have looked at some of the cu's and note that they are all full rcbo protected and have mains supply tails of 10mm2 copper. The main earth is 10mm copper glanded to what i thing is steel wired armoured cable ( all plasterd in. The main fuses range from 60 to 100A bs1361 type II.
Now if i use the 100A and the adiabatic. 904 x 904 x 1.3 square rooted, divided by 93(swa) that equals, 11mm2. How can i work out if the steel wired armour is adequate for the job, or am i buggered.
They were all periodically tested last year.
Thanks