    Hi everyone,

    I have an upcoming project that I would like some advise on please...

    I am going to be redecorating a bedroom which only has one double socket at present. I would like to add an additional two double sockets on different walls. My initial thought was that I would do a nice and easy fused spur to accommodate these sockets. However, I have had a peek at the socket and can see that it has 3 x cables already there, suggesting that it has already had a spur fitted from this socket (I am yet to lift the floorboards to try and trace everything).

    With this in mind, I was considering my other options. Mainly breaking into the ring main and spurring (via a connector) instead. Below is a couple of (rough!) drawings of my plan and a possible alternative). Would I be able to get some opinions as to whether I am looking at a suitable option please?

    Many thanks

    Option 1:

    [​IMG]

    This seems like the most sensible.

    Option 2:

    [​IMG]

    This seems like the easiest option as I dont need to fuse the spur as I am only have one double socket on each spur. However, I am not sure if I am allowed to break into the mains twice on the same run between sockets. I haven't read anything to suggest I can't, but I also haven't ready anyone else saying this method is acceptable.

    Many thanks
     
    Last edited: 19 Oct 2020
  2. Sponsored Links
  3. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,281
    Thanks Received:
    1,706
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    screwfix do a grid socket so a double socket box has in essence two single sockets in a double socket face plate, so you can take two spurs from a ring without having more than 3 cables in one terminal, over 3 cables you can end up with one cable not being fully clamped so should be avoided.

    Same grid socket would also allow a socket, a fuse and a switch in same double socket face plate, so you could have a socket and a fused connection unit in one double socket box.
     
    • Thanks Thanks x 1
  4. mjgreen81

    mjgreen81

    Joined:
    5 Oct 2014
    Messages:
    78
    Thanks Received:
    3
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Interesting. Thank you.

    Do you have a link for this item? I can't seem to find it.
     
    • Like Like x 1
  5. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    73,582
    Thanks Received:
    4,242
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    Do the cables run under the floor, or in the wall?
     
    • Thanks Thanks x 1
  6. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    73,582
    Thanks Received:
    4,242
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    • Thanks Thanks x 1
  7. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,456
    Thanks Received:
    2,116
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Option 3 is to - once you have identified the ring - extend the ring.
     
    • Thanks Thanks x 1
  8. mjgreen81

    mjgreen81

    Joined:
    5 Oct 2014
    Messages:
    78
    Thanks Received:
    3
    Location:
    Hertfordshire
    Country:
    United Kingdom
    I'm pretty sure they are under the floor (not lifted carpet yet)
     
  9. mjgreen81

    mjgreen81

    Joined:
    5 Oct 2014
    Messages:
    78
    Thanks Received:
    3
    Location:
    Hertfordshire
    Country:
    United Kingdom
    I need two sockets (the next one in the ring) to do this correct?

    I want to avoid lifting carpets/floors in other rooms.
     
  10. Sponsored Links
  11. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    73,582
    Thanks Received:
    4,242
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    if you can lift the floor and get at the cables, you can most likely interrupt and extend the ring with no need for junctions or spurs.
     
    • Thanks Thanks x 1
  12. mjgreen81

    mjgreen81

    Joined:
    5 Oct 2014
    Messages:
    78
    Thanks Received:
    3
    Location:
    Hertfordshire
    Country:
    United Kingdom
    As above, I need access to the adjacent socket to do this right?
     
  13. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,817
    Thanks Received:
    1,962
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Unlikely - there are 2 ring cables to the existing socket, identify the longer one and relocate it to a new socket, then add one or more sockets between those. No junction boxes, FCUs or spurs required.
    Floor will need to be lifted - but that will already have been done to get those cables in there, so it shouldn't be particularly difficult.

    Concealed junction boxes should be avoided, even if they are MF ones.
     
    • Thanks Thanks x 1
  14. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    73,582
    Thanks Received:
    4,242
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    depends on length of available cable, and where you want the new sockets.

    If you have socket A on the left, and socket B on the right, with a cable running A-B

    you want, instead, to have a cable running A to new1, from new1 to new2, and from new2 to B

    Sometimes if you cut cable A-B, it has enough length to reach from A to new1
    and enough length on the other side of the cut to run from new2 to B
    And you just insert a new piece from new1 to new2

    This method can be very easy in kitchens where there is a row of sockets and switches set 150mm above the worktop.

    If there is not enough length, you will have to run new cable to at least one of the old sockets.

    When you look behind the sockets and under the floor, you will see if oval conduit was used (very easy to poke new cable up) or plasterers capping (difficult) or clipped and plastered (needs chasing out).
     
    • Thanks Thanks x 1
  15. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,281
    Thanks Received:
    1,706
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    • Thanks Thanks x 1
  16. mjgreen81

    mjgreen81

    Joined:
    5 Oct 2014
    Messages:
    78
    Thanks Received:
    3
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Ah, I think I understand what you mean.

    Something like this?:

    [​IMG]
     
  17. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,456
    Thanks Received:
    2,116
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Exactly.
     
    • Thanks Thanks x 1