Balancing a radiator system that only seems to work in reverse ?

Joined
17 Apr 2019
Messages
13
Reaction score
0
Country
United Kingdom
I have 17 rads with TVRs, a Vitoden 111-w boiler fitted last year .
Have been trying desperately to balance my system over three days without much success to be honest . Have had all rad valves and lock shields fully open and know that all rads conduct heat , the issue is balance . I bought myself a temperature gun and started going from the closest rad first closing down the lock shield to get the 10-12 degree balance with the TVR fully open … yes , I do get all the rads to heat or at least get luke warm but cannot seem to get a good balance of real heat out of the rads at all ? If I start setting up the rads in reverse where I close down the TVR and then open the lock shields I get real heat out of the rads ??? It’s Been suggested the flow rate of water from the boiler needs increasing as well as possibly the temp , but not really sure … any ideas ? I got an engineer coming Wednesday for its first service so if I could get some suggestions and then get him to adjust flow rates if that is the answer .

Odd this one
 
What is the total rated output of the 17 boilers?
What boiler (Target) Flowtemp are you balancing with and to what dT?, I see its to 10/12C?
With all 17 rads in service what is the boiler output (if displayed) and what are the boiler flow/return temp, again if displayed?
 
Start by fully closing all the lockshields.

Then open them by half a turn, no more. Do they all start to warm up?
 
To balance a system with TRVs you need to open all the TRVs fully, then adjust the lockshields to achieve the desire temperature drop. Ideally, start with the index radiator, which is the one furthest hydraulically from the boiler. Once balanced adjust the TRVs to the desired room temperatures. With TRVs with 1 to 5 settings, Bedroom on 3, living room / dining room on 4 to 4.5, others as you see fit.
 
Oh dear, it seems no one can agree how? This is not a surprise, as I found what worked in late mothers house did not work with this house, so there is no one method works with all.

I do have a differential thermometer but I have lost the sensors, so I tried to use a thermometer.jpg point and read, this simply did not work, it looked as if it should, but it was no a steady enough reading.

I tried closing closest to boiler up-stairs first, and then opening ¼ turn at a time, feeling the pipes until just a little warmth felt and stopping, it was an improvement, but not ideal.

So I used the readings on the TRV heads, Flat Battery TRV.jpg the current should never exceed target, unless there is alternative heating. So I would watch when heating started up, in late mother's house, and if it was to over shoot, close it a little. It took nearly the whole winter to set them all up A1, but it did work.

So now thinking I knew how to do it, tried repeating in this house, and it failed, had to open each lock shield about 2 turns each, I assume the difference was due to this house has an oil non modulating boiler using micro bore, and mother's house a gas modulating boiler using 15 mm pipe work.

My sons first house again a gas modulating boiler, and he left the lock shields wide open and the boiler running 24/7 and it seemed to work A1, until he went on holiday, then it would not start up again. What I think was happening was the first radiator was heating up, and allowing hot water back to the boiler, which in turn caused the boiler to modulate, but with my house, since the boiler does not modulate, wide open would still work.

So maybe better to consider why we balance the radiator, and not just one reason.
1) On start up, it will allow all radiators to get some heat.
2) The radiator will heat up slow enough so the TRV valve can close it fast enough to stop it over shooting.

However, in my house, I have set the TRV heads in sequence, it only needs 10 minutes between them, for it to work, when using electronic TRV heads, much longer and the return hot water will cause the boiler to close down. But a modulating boiler will not react in the same way.

Even gas and oil will react different to each other.

It seems likely your problem is the boiler is modulating, due to hot water returning to boiler, which in turn is messing up your readings.
 