Not only, per your prediction, does it say "need not be connected...", but the whole of 411.3.1.2 relates (only) to the required bonding of extraneous-c-ps,
Exactly, so there is no need to mention the insulating section at all and the instruction to bond on the consumer's side of the meter, whatever the reason, is just wrong.
Exactly, so there is no need to mention the insulating section at all and the instruction to bond on the consumer's side of the meter, whatever the reason, is just wrong.
It's in the current OSG (yellow), two separate paragraphs for main and supplementary bonding.
A sad state of affairs when it is necessary to inform people who are supposed to have a moderate level of electrical knowledge that connecting wires to plastic pipes is not required.