I returned to the UK in the 1990s to find RCDs, RCCDs, ELCB-v, ELCB-c and the list goes on, with many names for basic same devices, it would seem in the main due to plastic water mains meaning the water main could no longer be used as an earth, and also the sixteen edition had been made into BS 7671:1992, and every electrician it seems had been on a course and was quoting what it said.
It was 2008 before RCDs were required for items within the home, before that we were fitting them for sockets likely to be used in the garden, but the rules said things like "(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit (iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation" but this was read by many as allowing us to use just two 30 mA RCDs, and before that with 100 mA RCDs were used for the whole house.
So as
@pete01 says, we should arrange it so we are not plunged into darkness, when a fault on the ring final trips the RCD. We used to split the ring finals side to side of the property, so if there was a failure, there was no temptation to run extension leads up or down stairs, but to get away with just two RCDs this changed, to split up/down so it could match the lighting circuits.
So in this house, split side to side, for ring final, and up/down for lights, it would need 3 RCDs, or use RCBOs which is a RCD and MCB combined. But most homes just had two, and reports on this forum tells us many people did not have a problem with that. I did, I would have the RCDs trip maybe 4 times in 2 weeks, no fault found, and then would run for maybe 4 years before it tripped again.
So this house when fuse box was replaced with a consumer unit, I had all RCBOs, and latter also an EPS (like a UPS but slightly slower change over times) to feed my freezers. In 5 years, one RCBO failed, I had 3 of the RCBOs trip, 2 of them good cause, one never did find out why. So I am glad I spent the extra for RCBOs, a bit annoying, hardly been fitted all type AC, when type AC were replaced with type A, I have upgraded 2, but have 12 left in the board.
You also have type AC and rated at 80 amps, as long as incoming DNO fuse 80 amps or less, that's OK, as to being type AC, with a TN supply the RCD is secondary protection so would not worry, but with a TT supply would consider an upgrade. But unlike I would bother.
However, there is nothing wrong with what you have, and I would only consider an upgrade if having problems with the existing setup.