You have plenty of spare capacity.
For instance, there are two (B16) radials "socket below" and "loft radial"
They could be combined to free one slot, or they could be made into spurs from ring finals, so that would give you 2 spare, plus the hole that should have a blank, plus the B6 on the left that is marked as spare.
Simples
For instance, there are two (B16) radials "socket below" and "loft radial"
They could be combined to free one slot, or they could be made into spurs from ring finals, so that would give you 2 spare, plus the hole that should have a blank, plus the B6 on the left that is marked as spare.
Yes, move the cable to the spare B6, or swop the B32 for the spare B6 MCB.Think that's actually 1.5mm on the 32A. For the lights on the ground floor. Think I'll change that!
Simples