People,
As part of my kitchen install, my elecrician has insisted that I must fit flexiable heat resistant cable between the oven cable connection plate and the oven
I have run a 6mm cable from the CU to a 45A oven switch then 6mm from the oven switch to the oven cable connection plate. Unfortunately, I have only been able to source 4mm cable in a short length of the flexible cable he requires.
The oven is to be a 7.2KW double oven so I presume 4mm will be acceptable. I propose to stick a sticker on the 4mm flexiable cable that says the following:-
" This particular cable is 4mm2. The cable from the Consumer Unit to the oven switch is 6mm and the cable from the Oven Switch to the oven cable connection plate is 6mm. In the event that an oven with power requirements above 7.2KW is installed, this particular cable shall require upgrading in size. A higher rating MCB may also be required in the Consumer Unit"
Please tell me whether you consider the above text seems appropriate. I am aware there has been some debate about the requirement for the said flexiable cable, but as he has specifically instisted I fit it, I don't wish to say there is a debate as to whether it is required or not!!!
Kind Regards
Paul
As part of my kitchen install, my elecrician has insisted that I must fit flexiable heat resistant cable between the oven cable connection plate and the oven
I have run a 6mm cable from the CU to a 45A oven switch then 6mm from the oven switch to the oven cable connection plate. Unfortunately, I have only been able to source 4mm cable in a short length of the flexible cable he requires.
The oven is to be a 7.2KW double oven so I presume 4mm will be acceptable. I propose to stick a sticker on the 4mm flexiable cable that says the following:-
" This particular cable is 4mm2. The cable from the Consumer Unit to the oven switch is 6mm and the cable from the Oven Switch to the oven cable connection plate is 6mm. In the event that an oven with power requirements above 7.2KW is installed, this particular cable shall require upgrading in size. A higher rating MCB may also be required in the Consumer Unit"
Please tell me whether you consider the above text seems appropriate. I am aware there has been some debate about the requirement for the said flexiable cable, but as he has specifically instisted I fit it, I don't wish to say there is a debate as to whether it is required or not!!!
Kind Regards
Paul