What's the rating of the cooker? Is there a socket?
I tend to take diversity with a pinch of salt
A 16A MCB with 30A being pulled through it probably won't hold in for long.
20A a bit longer.
Diversity takes into account not everything will be on at once but doesn't account for cold Xmas turkey
not questioning it , according to the figures ive given , when applying diversity is IB<IN<IZ , im new to this and i was taught that you apply diversity when working out cooker circuits to get you design current, mcb rating and cable current carrying capacities , dont get you nickers in a twist . I know the cable could do with changing, i just want to ensure the one ive got is going to be safe.
At the moment there is a possibility of overloading the cable as design current < fuse size < cable rating as installed thing isn't fulfilled.
When working out max demand by all means use diversity across all circuits, it just seems to me at times you can end up with a rediculously small figure if you use the OSG and need to apply common sense a bit.
Personally I think a 20A MCB for a 30A item might be problematic so I wouldn't do it, someone else might say it is fine.