Hi ,
I am installing a built in oven and seperate hob...The hob rating is 4.2kw max and the oven is 7.2kw max . which brings me to 11.4kw ..
I have a cooker control unit with red switch and a control unit at back of my old cooker ..
Now at my consumer unit the cooker i have now is protected with a 32amp fuse as the cooker is on it's own circuit.
Now at 240v and 11.4kw that would be 47.5 amps if my calculating is correct lol .
Would i be able to install the above hob and cooker at the one connection box .
I was thinking that using diversity it would work out at 26.25 amps as i am including 5 amps for the socket with the ccu using 6mm twin and earth.
The appliance is near the control outlet so is in the 2m zone specified.
Now i won't be using the cooker and hob at full potential so would this be ok to use this way ??
Also if this is ok can i use a 6mm cable from control unit to oven and another 6mm cable from same control unit to hob or would i be able to add one of these even though it says 45amp
http://www.alertelectrical.com/prod/1022/click-45a-easyfit-dual-appliance-outlet-plate
I know i could get someone in to upgrade my fuse at the consumer unit say to 45a, but as long as i am not using all the ovens and hob at the same time then would this work as mentioned above ??
Thanks inadvance ..I thought i would check here with you guys before anything is fitted.
I am installing a built in oven and seperate hob...The hob rating is 4.2kw max and the oven is 7.2kw max . which brings me to 11.4kw ..
I have a cooker control unit with red switch and a control unit at back of my old cooker ..
Now at my consumer unit the cooker i have now is protected with a 32amp fuse as the cooker is on it's own circuit.
Now at 240v and 11.4kw that would be 47.5 amps if my calculating is correct lol .
Would i be able to install the above hob and cooker at the one connection box .
I was thinking that using diversity it would work out at 26.25 amps as i am including 5 amps for the socket with the ccu using 6mm twin and earth.
The appliance is near the control outlet so is in the 2m zone specified.
Now i won't be using the cooker and hob at full potential so would this be ok to use this way ??
Also if this is ok can i use a 6mm cable from control unit to oven and another 6mm cable from same control unit to hob or would i be able to add one of these even though it says 45amp
http://www.alertelectrical.com/prod/1022/click-45a-easyfit-dual-appliance-outlet-plate
I know i could get someone in to upgrade my fuse at the consumer unit say to 45a, but as long as i am not using all the ovens and hob at the same time then would this work as mentioned above ??
Thanks inadvance ..I thought i would check here with you guys before anything is fitted.