Dual fuel cooker running on 13A plug for 16 years. Would similar replacement be OK?
3 Mar 2013
London
Hi All,
I’ve had a Hotpoint HUD61P dual-fuel cooker (gas hob, two electric ovens) for around 16 years, connected via a standard 13A three-pin plug into a dedicated socket behind it, installed this way by the original builders ~2010. There’s also a red cooker isolation switch on the wall.
Despite the original cooker being rated at approximately 4.8kW, it’s worked fine without any apparent electrical issues throughout that time. We only use one oven.
Since it’s now discontinued, I’m considering replacing it with a Hotpoint dual fuel HDD6GDC2WX, rated slightly lower at 4.4kW.
My question is, given that the existing cooker has worked perfectly well on this setup for 16 years, could the replacement realistically work just as well, particularly as we’d continue using only one oven? Or is there a significant difference I’m overlooking?
Appreciate that the manufacturer specifies hardwiring, but interested in the practical electrical reasoning and experiences of electricians who’ve encountered similar setups.
Thanks in advance
Is the socket fed by the cooker switch or part of a ring or radial circuit
Is the socket fed by the cooker switch or part of a ring or radial socket
The cooker plug socket (behind cooker) is definitely fed by the cooker switch above worktop, but not 100% if just the cooker in isolation all the way from the consumer unit, or any other switches on the ring as well. (If i've understood the question correctly)
Basic idea is, used for a short time, a BS 1363 socket can supply 3 kW, for a long time this is reduced to 2 kW, mainly as the socket now has insulation on the live pins, so it can't transmit as much heat to the socket, and also typically now white, not brown so again can dissipate less heat, however with the plug in forced air from an oven, it can likely dissipate a bit more heat, but that does not mean one can exceed the 3 kW limit.
It would have been drawing 19 amps, which is not really an option.
If you look at the consumer unit and there is a circuit breaker marked as being for the cooker then it sounds like a socket has been used instead of a cooker connection unit. If that's the case then you can change it for the proper unit and remove the chance of the plug and socket being overloaded and burning. If an electrician is doing the instalation for you he will make other checks and do that for you.
Not sure you can choose when to use and when to ignore diversity like that.
I see no way one can use 1.5 ovens, your using either 1 or 2, and although the ovens will heat using a mark/space ratio, one really has no option but calculate for both to be in use together, unless there is some built in system like in the old baby belling.
On the other hand, with 4 ring induction hobs, the power into the pan is restricted as too much will burn food, so even with 3kW rings, we know hard to get a load over 4 kW for the lot.
So if a cooker has 2 ovens and a hob, how does the calculation work?
The HUD is not supposed to be supplied via a plug and socket, because it has two ovens that can be used at the same time.
This is quite common, even on dual fuel cookers. There are others that have only one oven and can be plugged in.
Red flag here^^^^^^^
Need to find out how the socket is supplied. If it is fed direct from the cooker switch (and if the circuit protection in the CU is large enough) then change the socket for a cooker connection plate and wire the new one direct.
But needs more detail on the actual situation
By chance, I also have a rebadged HUD. My previous dual-fuel cooker was single-oven, with a plug, and I simply fitted a single socket to the cooker outlet. When I bought the HUD, I took the socket off.
Very likely, after verifying the circuit, OP can do the same. If the original cooker outket has been removed, and it is on a cooker circuit (not a socket circuit) a new outlet can be fitted.