You've often written that, but I've never understood. In the original version of BS7671:2018 (and probably earlier editions), not only did the sentence in question have "a full stop before it", but the one sentence constituted the entirety of a paragraph, namely ...Agreed, seen it many times, the old regulation had a full stop before it referred to single core cables, which some selected not to see ...
This statement explicitly singling-out of "single-core cables" surely meant that, in a multi-core cable, it was permitted for a G/Y conductor to be used for something other than a protective conductor,with overmarkings' (over-sleeving) at the terminations, didn't it? (514.4.3 relating to PEN conductors) ... so what is this that you always say about 'the full stop'??Single-core cables identified by green-and-yellow throughout their length shall only be used as a protective conductor
and shall not be overmarked at their terminations, except as permitted by Regulation 514.4.3.
As you say, that statement was changed in Amd 2 of BS7671:2018, such that it now reads (with my emboldening) ...
...so that the prohibition of oversleeving G?Y and using it as a live conductor is now prohibited in multi-core, as well as single-core, cablesSingle-core cables and conductors in multicore cables identified by green-and-yellow throughout their length shall only be used as a protective conductor
and shall not be overmarked at their terminations, except as permitted by Regulation 514.4.3.
If the G/Y conductor is not oversleeved at its terminations, that means that G/Y markings are being used to 'identify it', and that has never been allowed if it is being used as a live conductor........ I have many times looked in a wiring centre to see green/yellow not used as an earth.
514.4.2 Protective conductor
The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor and this combination shall not be used for any other purpose ...