I'm after some clarification please?
We have a TT system with an RCD, and as far as i can understand from the 17th regs (411.5) says that the maximum earth loop impedance on a TT system for 230V with a 30Ma RCD installed is 1667. It also says that anything above 200 would be unstable, with water and frost affecting its stability. Is this correct?
I ask, as today we had a repair guy turn up to fix a warranty fault on our tumble dryer.
As soon as we told him the fault, he said he didn't have the parts and never looked at the machine. Instead he plugged in an earth loop detector into a couple of sockets in the house (I wasn't around), and said as the results were above 200 he wouldn't be fixing the fault on the tumble dryer until we got a cert off a qualified engineer saying the electrics were safe.
Why he tested the home electrics and what's it got to do with a repair of a tumble dryer i have no idea, and i wish i was at home! As he had a pre-designed form to print off, I suspect this is common response. The form doesn't have an exact reading.
British Gas, replaced our meters a couple of months back with smart ones, and did various tests, so I would have thought that if there was a problem it would have shown up then.
I don't want to pay for a electrician only to find that there is no problem.
We have a TT system with an RCD, and as far as i can understand from the 17th regs (411.5) says that the maximum earth loop impedance on a TT system for 230V with a 30Ma RCD installed is 1667. It also says that anything above 200 would be unstable, with water and frost affecting its stability. Is this correct?
I ask, as today we had a repair guy turn up to fix a warranty fault on our tumble dryer.
As soon as we told him the fault, he said he didn't have the parts and never looked at the machine. Instead he plugged in an earth loop detector into a couple of sockets in the house (I wasn't around), and said as the results were above 200 he wouldn't be fixing the fault on the tumble dryer until we got a cert off a qualified engineer saying the electrics were safe.
Why he tested the home electrics and what's it got to do with a repair of a tumble dryer i have no idea, and i wish i was at home! As he had a pre-designed form to print off, I suspect this is common response. The form doesn't have an exact reading.
British Gas, replaced our meters a couple of months back with smart ones, and did various tests, so I would have thought that if there was a problem it would have shown up then.
I don't want to pay for a electrician only to find that there is no problem.