Howdy chaps,
Had an eicr carried out today which failed on the following:
Observation 1 — C1
Protection against mechanical damage where cables enter consumer unit/distribution board (522.8.1; 522.8.5; 522.8.11)
Observation 3 — C3
Coordination between conductors and overload protective devices (433.1; 533.2.1) light circuit in 16 A mcb
Also mentioned the exposed tails for remedial action, but did not give a code for this.
Been quoted £510 to carry out the following remedial works:
EICR Remedial Works Required: 1. Replace 2 x rcd 2. Fi on upstairs cpc discontinuity 3. FI on cpc continuity on upstairs lights , if no cpc present replace switch to plastic 4. Install grommets 5. Move light circuit to 6 A mcb 6. Terminate the incoming meter tail with no copper exposed
Pricing
Is this classified correctly and reasonable cost to remedy the problems?
Thanks
Had an eicr carried out today which failed on the following:
Observation 1 — C1
Protection against mechanical damage where cables enter consumer unit/distribution board (522.8.1; 522.8.5; 522.8.11)
Observation 3 — C3
Coordination between conductors and overload protective devices (433.1; 533.2.1) light circuit in 16 A mcb
Also mentioned the exposed tails for remedial action, but did not give a code for this.
Been quoted £510 to carry out the following remedial works:
EICR Remedial Works Required: 1. Replace 2 x rcd 2. Fi on upstairs cpc discontinuity 3. FI on cpc continuity on upstairs lights , if no cpc present replace switch to plastic 4. Install grommets 5. Move light circuit to 6 A mcb 6. Terminate the incoming meter tail with no copper exposed
Pricing
| Labour £300 |
| Materials (EICR remedial materials) £180 |
| Recalibration £20 |
| Sourcing Fee £10 |
| Total £510 |
Is this classified correctly and reasonable cost to remedy the problems?
Thanks