I had exactly the same problem - locating the TF1 on return was virtually impossible. So I emailed Fernox and asked their advice. They replied:
There is no objection in principle against installing on the flow side.
The main reason for not recommending the flow side seems to be that, if the valves were accidentally left closed, a potentially dangerous situation could arise.
There should be no valves between the boiler and the open vent and cold feed. This is why it is sometimes incorrect to fit a TF1 or magnaclean on the flow pipe adjacent to the boiler. If it is a sealed system or fitted after the vent/feed it's not an issue other than providing slightly less protection to the boiler.