Fiddly Kitchen Socket

Presumably each module has to be linked with short bits of wire, which could be very awkward in some installations.

Bad design really.

Where'd you find that then?

Homebase?
 
Yeah... I did think the two sockets might have one set of terminals...:(
 
:) An absurdity! On the other hand, manufacturers are allowed to protect 0.75 with a 13A fuse.

It's running a wall wart for a DECT phone and a 5.22A toaster. So the load it is carrying is less than a lighting circuit of 6A. Plus, the 1milli is a maximum of half a meter in length.
 
:) An absurdity! On the other hand, manufacturers are allowed to protect 0.75 with a 13A fuse.

It's running a wall wart for a DECT phone and a 5.22A toaster. So the load it is carrying is less than a lighting circuit of 6A. Plus, the 1milli is a maximum of half a meter in length.

So what about when someone comes along and plugs in a kettle next to the toaster? OK the FCU fuse goes and they replace it with a 13A one. Then what?
 
It's running a wall wart for a DECT phone and a 5.22A toaster. So the load it is carrying is less than a lighting circuit of 6A. Plus, the 1milli is a maximum of half a meter in length.
Maybe, but that's common sense. I'm talking regs, and it's not compliant! Have I got any 1mm² cable in my house other than in lighting circuits? .... no comment :) Would I actually ever wire a BS1363 socket, via a FCU, with 1mm²? ... perhaps not, but probably mainly because of the regs (and the possible scenario mentioned by winston).

Kind Regards, John
 
Last edited:
But as has been said before that reg., Table 52.3, makes no sense.

To be compliant with 1mm² (or 0.75mm²) ss could have used "Non-sheathed or sheathed flexible cable" instead of "Non-sheathed or sheathed cable".
 
I used the 1 milli as it was there and to replace it would mean smashing tiles off the wall.

If I put a 13A fuse in the FCU, so what?

The rating of 1 milli is?
 
But as has been said before that reg., Table 52.3, makes no sense.
It doesn't - but, if one assumes that a "power circuit" is anything which is neither a "lighting circuit" nor a "signalling or control circuit", it is otherwise clear what the regulation is saying/requiring (i.e. what it "actually says"), even if it makes little sense.
To be compliant with 1mm² (or 0.75mm²) ss could have used "Non-sheathed or sheathed flexible cable" instead of "Non-sheathed or sheathed cable".
He could. As we have agreed, it makes little sense - but that's not a problem peculiar to this one regulation.

Kind Regards, John
 
I used the 1 milli as it was there and to replace it would mean smashing tiles off the wall. If I put a 13A fuse in the FCU, so what? The rating of 1 milli is?
Assuming no 'extreme' installation method a 13A fuse would adequately protect 1mm² cable. However, the regs require Iz≥Ib, as well as Iz≥In, so you would have to be able to argue that the "design load" of 2 x BS1363 outlets was less than the CCC of the cable. Of course, if there were just a single BS1363 outlet (even without an FCU), that condition would usually be satisfied, even though Table 52.3 would still not be happy with 1mm² T+E for a 'power' circuit.

Don't forget, as we've discussed before, that it probably takes around 22A to blow a 13A BS1362.

Kind Regards, John
 