    Hello, I've recently experienced a problem with the above boiler. Boiler is 10 years old and has become noisy. Gas engineer put Fernox F2 boiler silencer into system. This exposed a noise which sounds like drums being played inside the boiler! This only occurs when the boiler is fully surging in power, usually around 70 degrees. The HEX has been cleaned, fan replaced and now system is being cleaned with Fernox F3. The diverter valve is sticking slightly and is being replaced next week. I took a video illustrating the noise this pm after the cleaner had been applied. Here the boiler is surging before it cuts out. Can anyone identify the noise?

    https://1drv.ms/v/s!Aq7r42kkeO1ngs4GzkON-AfGf-qs_A

    Thanks for any advice

    Tony
     
  2. Sponsored Links
  3. easyflow

    easyflow

    Joined:
    12 Jan 2008
    Messages:
    472
    Thanks Received:
    60
    Country:
    United Kingdom
    At a good guess I would say the problem lies not with the boiler but an iron oxide blockage probably with the flow or return around the cylinder area.
    Ask your plumber to run a magnet all over the the flow and return pipes in the cylinder cupboard, see if the magnet pulls at a certain point(s).
     
  4. tonygima1

    tonygima1

    Joined:
    26 Jun 2018
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for that, will follow that up.
     
  5. MTCH

    MTCH

    Joined:
    1 Mar 2018
    Messages:
    31
    Thanks Received:
    1
    Country:
    United Kingdom
    What was done to clean the heat exchanger?
     
  6. tonygima1

    tonygima1

    Joined:
    26 Jun 2018
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    The burner door was removed and scale removed using a nylon brush with a mixture of strong white vinegar and limescale remover. All surfaces were smooth and scale free when the door was replaced. Now running Fernox F3 through the system for a week.

    Many thanks

    Tony
     
  7. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,758
    Thanks Received:
    3,073
    Location:
    Sussex
    Country:
    United Kingdom
    What's the bypass valve set to and the pump setting? If the boiler is installed correctly it should be across the flow and return after the pump...it ensures a minimum flowrate through the boiler.
     
  8. 45yearsagasman

    45yearsagasman

    Joined:
    14 Mar 2010
    Messages:
    6,085
    Thanks Received:
    1,090
    Location:
    Norfolk
    Country:
    United Kingdom
    The heat exchanger was removed and cleaned with chemicals internally I hope. Removing the cover and polishing the combustion surfaces will do SFA to reduce noise.
     
  9. tonygima1

    tonygima1

    Joined:
    26 Jun 2018
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Not sure about the bypass valve setting, pump is on maximum. Fernox F3 is running in system at the moment (leaving up to 7 days) to remove limescale
     
  10. Sponsored Links
  11. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,758
    Thanks Received:
    3,073
    Location:
    Sussex
    Country:
    United Kingdom
    And you're not going to check it or post a pic of the setting?
     
  12. tonygima1

    tonygima1

    Joined:
    26 Jun 2018
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    I'm a novice, not a plumber/gas heat engineer so not sure where bypass valve is
     
  13. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,758
    Thanks Received:
    3,073
    Location:
    Sussex
    Country:
    United Kingdom
  14. Hason

    Hason

    Joined:
    3 Apr 2015
    Messages:
    140
    Thanks Received:
    14
    Location:
    Bournemouth
    Country:
    United Kingdom
    It will be a coil in the heat exchanger partly blocked, hxi heat exchanger has coils. You can not clean heat exchanger, new heat exchanger required just done 2 , I cut them open scale/debris wedged in coil.
    Hopes this helps
     
  15. tonygima1

    tonygima1

    Joined:
    26 Jun 2018
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Many thanks for your response. Have discovered that cold feed and expansion pipes are partially blocked (used powerful magnet). Work being done next week.
     
  16. ServiceNumpty

    ServiceNumpty

    Joined:
    9 Sep 2007
    Messages:
    6,718
    Thanks Received:
    1,612
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Be prepared to shell out for a new heat exchanger then. If the system was dirty as it sounds like it is, the waterways in the giannoni hex are tiny and block up very easily.
     
  17. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page