    http://www.voltimum.co.uk/news/1962...m=email&utm_campaign=2013_04_15_VLT_VoltiTECH

    Apart from the idea that there are ends to a ring (?), surely the first test of the circuits themselves is dead continuity. So at the MCB there would be continuity through the two legs and nothing between either of those and any other circuit.
    Circuits can be accidentally connected but this would show immediately in a normal house.
    The danger of cross connection which is hard to detect is where there are two separate sources of power feeding one piece of equipment and one is isolated by a simple switch (e.g.PIR).
    Have I missed something?
     
  2. Sponsored Links
  3. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    There are when you break it to do tests.


    The standard test for continuity does not involve looking to see if there's continuity to other circuits.


    Depends on what testing is done. With none, it might never show.


    If you join two circuits you get all of the loads being shared by 2 devices, so your Ib ≤ In ≤ Iz breaks.

    It's even more acute with ring finals where you start with the idea that you can have a safe circuit where Iz is 20 and In is 32 because it's a ring.
     
  4. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,467
    Thanks Received:
    2,120
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Don't forget he is from Fluke and trying to sell his test equipment.

    We've all seen the results of DIY / uninformed / bad electrical work.
    Obvious examples that I come across - all too often are:
    Rings that are actually figure of 8
    Rings that have one leg in one MCB and the other leg in a different MCB
    Rings interconnected (kitchens is the best place to find this)

    All of these can be found by following proper testing procedures but (as we know) the mopst testing that is usually done is to
    "switch it on and if it works then everything is OK"

    And yet 'they' water down the one building regulation that should reduce this happening. :rolleyes:
     
  5. viewer

    viewer

    Joined:
    2 Apr 2005
    Messages:
    772
    Thanks Received:
    52
    Country:
    United Kingdom
    Not quite sure what cable/circuit design loading makes to the original comments on testing, but I'd certainly agree on the dangers of overloading and cross connections which make the ring final assumptions worthless. Give me a proper radial every time.
     
  6. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Design and loading comments were in reply to what you said about the danger of cross connecting.

    And it applies to radials too.
     
  7. Sponsored Links
  8. viewer

    viewer

    Joined:
    2 Apr 2005
    Messages:
    772
    Thanks Received:
    52
    Country:
    United Kingdom
    Ah yes; complete agreement.
     
  9. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,467
    Thanks Received:
    2,120
    Location:
    Oxfordshire
    Country:
    United Kingdom
    An unintended ring circuit then ;)
     
  10. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    If they were originally radials you'd end up with an unintended ring, two unintended unfused spurs, all supplied by 2 MCBs.

    Not good.
     
  11. OwainDIYer

    OwainDIYer

    Joined:
    5 May 2010
    Messages:
    4,548
    Thanks Received:
    696
    Location:
    Stirlingshire
    Country:
    United Kingdom
    I could make some comment about "professional electrician types" who left an entire block of flats unearthed ... connected a ring across two 20A MCBs ... etc etc etc.
     
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page