Taking your last drawing first - now my PC skills do not come near yours so I can't (or may be that should be - can't be bothered to try) produce diagrams like yours. So what to do - well I just go to the CCU terminations of my RFC and count how many conductors ends I can pull out. Next I could go to each socket outlet and do the same.
I really can't believe that you don't grasp the point I'm trying to make.
I'm not asking you how you would determine whether you had a ring or two radials.
I'm trying to explain to you, by getting you to think about continuity readings, the following:
1) If you get a reading of infinity, you have two separate conductors,
2) If you get a reading of a few hundred milliohms you have one separate conductor.
And you don't have to draw anything - you just have to answer my question about how many conductors there are at B, C, D etc, and the only PC skill you need to do that is the ability to type a letter, a space or other separator, and a number, on 7 consecutive lines.
Now its a great pity BAS that you were not on the 607 committees that met after the one I sat on - if you had been you could have helped them out. You see on the committee I attended we actually spelled out in plain English that 2.5mm² / 1.5mm² was adequate when used to form a RFC with a high integrity earth (see my earlier post). Since then they have used a form of words that is not so starkly obvious.
That must be the understatement of the year. They have used words so appallingly badly that they have written a requirement that is not what they mean, and a requirement which, in the way that it is written, does not allow a 2.5/1.5 ring if high integrity earthing is required.
The fact is,
you cannot count the conductors in a ring twice - there are not two phase or neutral conductors, there is one of each. They are in the shape of a ring, and the fact that at any point of use current will flow in two directions along each segment of them does not make each two conductors. There are not two cpcs, there is one. It is in the shape of a ring, and the fact that at any point of use current could flow in two directions along each segment of it does not make it two conductors.
If you try to use the argument that it does, then how many cpcs does 10mm² have? Seven, because that's how many strands there are, and therefore that's how many paths a cpc current could take?
If you're using the braid of an SY cable as a cpc, how many cpcs do you count that as?
By what logically inconsistent and plain-English incorrectness do you decide that if you take one conductor, and bend it round so that the ends touch, you now have two conductors?
I don't believe that a single one of all the questions I've asked you can be logically and consistently answered and not show that a conductor in the shape of a ring is still
a conductor. But I do believe that the realisation of that is why neither you nor anybody else has attempted to answer any of them.
Now the fact of the matter is that my view is supported by the industry in general - BTW some of the large national contractors that have installed these circuits in the way I have described - may be just a little irritated by the fact that you are implying that they have not complied with BS 7671, and are therefore, in breach of contract with many major clients
.
Well I'm all broken up about that. But they undeniably are in breach of BS7671 as it is written.
Just as an aside BAS - can you explain why high integrity earthing is sometimes required and the basic principles behind the protection it offers? If you can you may come to realise that, just in this case - size does not matter
.
Please don't think that I don't understand why it's needed, and why separate terminals are used etc - I'm simply pointing out that a ring final has only
one cpc, and
if that cpc is only 1.5mm², and
if high-integrity earthing is required, then according to BS7671 size does matter, at least to the extent that one cpc of 1.5mm² is not deemed to be adequate.