Thanks for clearing that up, numerical!
Here's a RFC:Now 602 - take a close look at 607-02-04 (iii) paragraph 2 - ring circuit (4 * 2.5) + (2 * 1.5) = ?
Any reason why the earths are terminated like that.
1) Dunno what the 17th requires, but mdbalson's kitchen is being done to the 16th.
2) The implication of the explanation in that Wiring Matters article is that confusion about the topology of a circle is not confined to members of this forum. A ring final circuit has one phase conductor, one neutral conductor and one cpc....
Topologically it is.A ring final circuit is not a circle
Topologically it is.
Please answer these questions:If I have two routes - each delivering energy from the source to the sink - I have the number of conductors I indicated.
Please draw us a ring final circuit with a source and 10 socket outlets. To make life simpler you may show just the phase, neutral or cpc elements.If I have two routes - each delivering energy from the source to the sink - I have the number of conductors I indicated.
Does that not mean where both individual CPCs are in the same multicore cable?The values I get are not relevant because I can engineer them to be what ever I like.
However, I am at the CCU and I have two 2.5mm² conductor ends in the mcb terminal (or perhaps terminus) - so that is 2 * 2.5 = 5.
Next I go to the neutral connection bar and I remove the 2, 2.5mm² conductors related to my circuit. 2 * 2.5 = 5
Then I go to the earth connection bar and - you guessed it - I remove the 2, 1.5mm² related to my circuit. 2 * 1.5 = 3
Now I wonder what (2 * 2.5) + (2 * 2.5) + (2 * 1.5) equals - do you know?
The sort of values, or orders of magnitude of the values you get are extremely relevant.The values I get are not relevant because I can engineer them to be what ever I like.
Let us assume that the conductor ends you have removed are those of a ring. When you connect your continuity tester to them to measure the conductor resistance, what order of magnitude would you expect the reading to be?However, I am at the CCU and I have two 2.5mm² conductor ends in the mcb terminal (or perhaps terminus) - so that is 2 * 2.5 = 5.
The values I get are not relevant because I can engineer them to be what ever I like.
However, I am at the CCU and I have two 2.5mm² conductor ends in the mcb terminal (or perhaps terminus) - so that is 2 * 2.5 = 5.
Next I go to the neutral connection bar and I remove the 2, 2.5mm² conductors related to my circuit. 2 * 2.5 = 5
Then I go to the earth connection bar and - you guessed it - I remove the 2, 1.5mm² related to my circuit. 2 * 1.5 = 3
Now I wonder what (2 * 2.5) + (2 * 2.5) + (2 * 1.5) equals - do you know?