sometimes, an experienced and consciencious amateur can be as reliable as a sloppy professional.
I agree, there are very good and very bad sparks!
sometimes, an experienced and consciencious amateur can be as reliable as a sloppy professional.
More important, he pointed out in horror that the new wiring system had never been connected to earth! He did it for her, there and then, at no charge.
The NICEIC do not make up regulations and that observation is almost certainly a lack of understanding by the contractor. It's a common one, made by most older electricians, because they do not understand that regulation 543.2.7 refers to using conduit as the CPC.Could be a NICEIC makey-upper? like compulsory earth fly-leads to back boxes which the absence of at a friend of mine's has just been given as a PIR code 2![]()
Yes it is, although it is unusual to see it done nowadays. Reg 543.1.2 refers to a circuit protective conductor common to two or more circuits.You used to be able to share earth conductors when running singles in conduit/trunk, this is no longer permissible either.
It would need to be done in minimum 4mm earth wireWould it be OK for the op to run separate earth cables to the metal fittings and connect them to the MET?
The NICEIC do not make up regulations and that observation is almost certainly a lack of understanding by the contractor. It's a common one, made by most older electricians, because they do not understand that regulation 543.2.7 refers to using conduit as the CPC.
It would need to be done in minimum 4mm earth wireWould it be OK for the op to run separate earth cables to the metal fittings and connect them to the MET?![]()
Easier to ditch the class 1 fitting and use a class 2 double insulated one.
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local