How unsafe are spurs?

Joined
14 Jan 2008
Messages
167
Reaction score
2
Location
Buckinghamshire
Country
United Kingdom
We have quite recently moved to a Victorian cottage.
As far as I can tell the front room and kitchen sockets are all fitted in a traditional ring on the same fuse. The trouble is that the dining room and utility room sockets are all fed off of a spur, thats 5 double sockets and 1 single socket!
They don't all loop off each other but are connected to various terminal boxes(http://www.screwfix.com/prods/15143/Electrical/Cable-Accessories/Junction-Boxes/Heavy-Duty-Junction-Box-20A-6-Terminal). For all intense and purposes though they are all on 1 big spur.
Is this unsafe? What will 2.4mm twin and earth take?
Cheers,
Chris
 
Sponsored Links
Is this unsafe? What will 2.4mm twin and earth take?

Are you sure they are a spur, and not a loop into a ring, or a figure 8?

If they are really on a spur, then they should be rectified. If you had a survey, this should have been noticed.
 
Are they all fed off individual spurs from the ring or do they share a common cable? What size MCB/fuse protects this circuit?
 
As far as I can remember (I'm at work now) it is all fed off 1 spur which is off the main downstairs ring. This is protected by a fuse with 15Amp wire in.
 
Sponsored Links
As far as I can remember (I'm at work now) it is all fed off 1 spur which is off the main downstairs ring. This is protected by a fuse with 15Amp wire in.

If it is all on a 15A then its not a problem. If it is on a 30A (like most rings are) then it is a problem and needs to be rectified, turned back into a ring or de-rating the fuse to 15A.
 
Thats great. At least I don't need to get it changed. I'll stick with the 15amp fuse wire.
I was worried about the cable getting hot and catching fire or something but looks like I could be safe!
 
I think it might still be an idea to get an electrician to have a look over the wiring.

Rewireable fuses and a circuit arrangement like the one you detail is often a sign of an ageing installation.
 
Are there any meaurements I can take to check for electrical safety?

I've got a decent multi-meter and am quite confident in its use so is there anything you can suggest?
 
If you had a survey, this should have been noticed.

Not necessarily.

When we bought Secure Towers, the survey was one of the top we could have, £900.

But as soon as the guy got in the front door, he said, we don't do gas we don't check appliances, we don't check plumbing, we don't check electrics.....
 
They don't always look in lofts. etc etc.

As far a testing you can do yourself with a multimeter, you're a bit limited. Electricians carry specialist, calibrated test equipment which can perform a lot of tests a multimeter can't.

I'd agree with RF and say get a Periodic Inspection Report done, not sure how much to pay as not only do I not do them on their own (only before major works) it will vary up and down this great land.

Better low-ohms conductor resistance measurement, earth loop impeadence, potential fault current measurement, RCD testing, Insulation Resistance measurement (or meggering) which is a really good one for getting an idea of the integrity of a cable/accessories.
 