    I have noticed a fault with my CH in that the grundfoss pump never stops running. It obviously can't be good for it and it's not quiet either and has become very annoying.

    I took the cover off the honeywell control box (look likes a junction box with different sections for wiring) and I can see the pump over run terminals have been used and the links you cut to configure have set it for pump over run also. I rang ideal to ask about pump over run and they said the icos doesn't have pump over run and there is no where on their boiler to connect it up anyway. Is that true? If so i'm a bit confuzzled how something has been wired in by means of where on earth do the other end of those wires go?! Anyone give advice on questions above and what i can do. I do have a multimeter.

    thanks

    :oops:
     
  2. Sponsored Links
  3. shambolic

    shambolic

    Joined:
    25 Aug 2008
    Messages:
    5,754
    Thanks Received:
    2,855
    Country:
    United Kingdom
    No pump overrun or need for bypass as the boiler has a fan overrun ! Please change thread title to pump staying on 24hrs when system switched off.
    Probably faulty end switch at one of your motorised valves!
     
  4. gas4you

    gas4you

    Joined:
    23 Feb 2007
    Messages:
    21,178
    Thanks Received:
    1,912
    Location:
    Norfolk
    Country:
    United Kingdom
    Is this a new installation?

    Sounds as though it has been wired wrong at the JB
     
  5. adwt2004

    adwt2004

    Joined:
    8 Nov 2006
    Messages:
    327
    Thanks Received:
    3
    Location:
    Bristol
    Country:
    United Kingdom
    There has been a pump overrun wired in and at the top right hand side link six has been cut for a pump over run. It's a year and a half old installation. Installed before i moved in. Should i take a photo of it, would that help?
     
  6. mickyg

    mickyg

    Joined:
    24 Aug 2005
    Messages:
    16,007
    Thanks Received:
    3,325
    Location:
    Cornwall
    Country:
    United Kingdom
    yeh pictures are always helpful. I'm interested as to if it has an option for a pump overun like you suggest. Surely if its an option it can be used. Maybe our resident Ideal expert can explain.
     
  7. gas4you

    gas4you

    Joined:
    23 Feb 2007
    Messages:
    21,178
    Thanks Received:
    1,912
    Location:
    Norfolk
    Country:
    United Kingdom
    The Icos, apart from the system version has no option for pump over run.

    I assume the pump over run we are talking about is in the Honeywell wiring center, the pcb version that you cut the built in links depending on your system set up.
     
  8. adwt2004

    adwt2004

    Joined:
    8 Nov 2006
    Messages:
    327
    Thanks Received:
    3
    Location:
    Bristol
    Country:
    United Kingdom
    Yes that's correct, The pcb has i think five terminals for a pump over run and they are wired in to. also link 6 at the top right hand side has been cut which according to the inside of the honeywell cover is for a pump over run. Ideal confirmed there is no pump over run on the boiler so i guess i need to find out where the wires are going. The pump is wired into another section on the honeywell board labelled pump.

    What a mess, i will post a pic
     
  9. gas4you

    gas4you

    Joined:
    23 Feb 2007
    Messages:
    21,178
    Thanks Received:
    1,912
    Location:
    Norfolk
    Country:
    United Kingdom
    Easiest answer is to buy a new Honeywell wiring center, then wire it properly for your system.
     
  10. Sponsored Links
  11. londonboy

    londonboy

    Joined:
    22 Feb 2009
    Messages:
    1,582
    Thanks Received:
    149
    Location:
    London
    Country:
    United Kingdom
    Or turn power off at spur, pull white sleeving off the two sides of the broken link (link 6), and twist the two wires together with pliers.
    I've never cut the wrong links :oops:
     
  12. adwt2004

    adwt2004

    Joined:
    8 Nov 2006
    Messages:
    327
    Thanks Received:
    3
    Location:
    Bristol
    Country:
    United Kingdom
    Been a long time but have to ask whether repairing the link that has been cut is all i need to do? I'm quite happy to sort it out and maybe solder it as access is easy but what about the wires that are in the pump overun terminals, do i just leave them in situ?

    I have some wires going into the pump terminals and another cable going into the pump over run terminals and link 6 is cut at present. Pump is contantly pumping but everything heating wise is working ok.
     
  13. adwt2004

    adwt2004

    Joined:
    8 Nov 2006
    Messages:
    327
    Thanks Received:
    3
    Location:
    Bristol
    Country:
    United Kingdom
    Here are the images, the black cable comes from my motorised valve and into the pump over run terminals according to the inside of the honeywell white cover. The pump is wired with a white cable to the standard pump terminals. And the links cut are shown. Can anyone help?

     
  14. adwt2004

    adwt2004

    Joined:
    8 Nov 2006
    Messages:
    327
    Thanks Received:
    3
    Location:
    Bristol
    Country:
    United Kingdom
    Just had another look and I believe i have an Y plan system. Three port valve
     
  15. londonboy

    londonboy

    Joined:
    22 Feb 2009
    Messages:
    1,582
    Thanks Received:
    149
    Location:
    London
    Country:
    United Kingdom
    Cut link L1
     
  16. adwt2004

    adwt2004

    Joined:
    8 Nov 2006
    Messages:
    327
    Thanks Received:
    3
    Location:
    Bristol
    Country:
    United Kingdom
    My wiring centre is wired with switched lives as per the diagram below


    Shouldn't it just be LNE connections? I've taken a look at the boiler manual http://www.idealboilers.com/docs/pdf/icos_he_manual.pdf page 24 and it does have room for 5 wires but i don't know why. Whoever installed it should be shot for doing it wrong, it was checked by a BC officer too, not what they know anything about boilers or controls.

    Cutting link 1 refers to a two channel programmer and the boiler always being switched on which it isn't. It's only the pump that keeps chugging away constantly.
     
  17. londonboy

    londonboy

    Joined:
    22 Feb 2009
    Messages:
    1,582
    Thanks Received:
    149
    Location:
    London
    Country:
    United Kingdom
    Your boiler has 5 terminals only 4 are required.
    Permanant live
    Neutral
    Earth
    Switchlive

    check connections at boiler and cross check with wiring centre.
     