There clearly are various ways in which the wording could be interpreted.Spurs are obviously part of the circuit but not part of the ring. ... Does the wording not say that "ring circuits must be done like {the following} whether or not there are spurs".One could say that. However, the requirements relate to 'the circuit' and I would have thought that most people (even the BS7671 definition!) would say that spurs were part of 'the circuit'. wouldn't they?
That's what we're discussing, isn't it? The spur cable to a double socket is being protected upstream by a 30/32A OPD (which would never be sufficient) and downstream by two plug fuses, both of which could be 13A (i.e. 26A total) - and the latter would not be adequate if the CCC of the spur cable was as anything like as low as the minimum permitted for the cable of the ring. Is it perhaps your belief that an unfused spur cable supplying a double socket must have a CCC of at least 26A (i.e. that 2.5mm² would only be acceptable if 'clipped direct')?I cannot see why the spurs, especially the without spurs part, are mentioned at all.
This whole sub-discussion arose because, in commenting about the total load capacity of a double socket, I 'innocently' suggested that (assuming it also applied to unfused spur cables!) the 20A minimum CCC for rings would be consistent with a view that a double socket was considered as a maximum load of 20A.
Quite so - you have already used the fact that ('guidance') App 15 is non-exhaustive to support your view that a 4mm² unfused spur (from a 2.5mm² ring final) supplying two or more sockets would be compliant (we don't disagree that it is certainly electrically satisfactory).I suppose not every option can be shown but a noted box, as with the other options, could be included.No electrical reason, really (given the downstream ≤13A fuse in the plug) - so maybe this is another example of a 'lack of exhaustiveness' in Appendix 15.
Kind Regards, John