Insulation resistance testing

Joined
15 May 2006
Messages
38
Reaction score
0
Location
Buckinghamshire
Country
United Kingdom
How do you do this on lighting circuits with lv donlight transformers attached to the circuit?

The junction boxes could only be accessed by removing ceilings in some places!!

TIA
 
Sponsored Links
resistance.jpg
 
Too much Star Trek :eek:

If my lights were on my space ship (already tested) commets would be OK!!!! ;)

As not advice would be great before something blows (other than the clingons :evil: )
 
Sponsored Links
Connedt Live to Neutral and just test between them and the CPC and mark it down as a limitation?
 
Where live to neutral? I am asking as we have LABC coming to test the electrics and their electrician seems a bit clueless and we dont want all the transformers blown, there being one on each light and the junction boxes being inaccessible save for the last one on each circuit.
 
AdamGT3 said:
Where live to neutral?
Connect live and neutral together and insulation test between these and earth.
there being one on each light and the junction boxes being inaccessible save for the last one on each circuit.
oops, all junction boxes/screw terminals should be accessable for Inspection and Testing.
 