Hi

My mum had someone install an extractor fan as part of an ECO scheme

From a safety and legal perspective are there any things of concern from the attached photos, and if so can someone please explain why, as this will be used as part of an official complaint


Thanks
 

Attachments

  • PXL_20241018_201310489.jpg
    PXL_20241018_201310489.jpg
    181.3 KB · Views: 292
  • PXL_20241018_201318340.jpg
    PXL_20241018_201318340.jpg
    151.3 KB · Views: 332
Wiring regulations, are not law, but can be used in a court of law, but it seems the parts of the building regulations are law, not saying I agree with the requirements of Part F, but we are now aware of the problems.
However, I have thinking work was being done within the building regulations, tried to get the work transferred, only to find the builder had not followed the law, and it seems I or at least my dad, as homeowner was responsible to ensure the correct applications had been made, and I found I was being told off for not registering the work, not the builder.

I wished I had never told the LABC, but you can't un-tell them. So although clearly not a professional job, you need to think twice before reporting the work.
 
From a safety and legal perspective are there any things of concern from the attached photos, and if so can someone please explain why, as this will be used as part of an official complaint
I would just say that the whole cable including the grey sheath should go into the fan.

However, that is such a disgrace that it is hard to believe anything could be done so badly.
 
Report them to trading standards.

Did they provide an invoice and certificate ?
 
It's so bad, it's just fascinating.

Anyone else can do better than this.

I bet there's even wires jointed in that trunking.

You can waste your time trying to report it - you can say the cable isn't fully sheathed. You say it's utter crap, which it is. But I doubt it will get you anywhere.

Whoever fitted that is NOT an electrician. Or even a trainee electrician.
 
It certainly does nothing to bring hope that they are capable of doing anything with anything. I would not trust them to clean my windows or tie my shoelaces.

Even if they have got some of the things technically correct then the appearance is so shoddy that it gives absolutely no confidence of anything they have touched.
 
Can't quite tell from the pics but is that 3c&e to the fan with brown and black only used in the trunking or do all the cores go to the fan?
The ridges on the inside of the sheath look like it might be 3c&e but have the grey and earth been cut back?
Defo needs redoing though and at no extra cost.
 
A proffessional did that?
Someone that was paid? (by someone)

I could do better than that when I'm so drunk I cannot see.
Awful workmanship.
Dodgy company as part of the eco scheme

My brother will meet them next week after I kicked off at them and apparently I'm a health and safety risk to them
 
From a safety and legal perspective are there any things of concern from the attached photos, and if so can someone please explain why, as this will be used as part of an official complaint
I see a couple of things in that picture that violate BS7671.

1. The inner insulation of the cable cores is exposed, this would generally be considered a "C2" ("potential danger") on an EICR. It is acceptable to run "single insulated" cores in trunking but if you do then much greater care has to be taken in constructing the trunking system than if sheathed cables are used.
2. There doesn't appear to be an earth wire taken to the equipment, I think I can just about see a bare earth wire entering the trunking, but I don't see one in the section with a missing lid that runs down to the fan. For a class 2 appliance, this would generally only be considered an "observation" on an EICR.

Now BS7671 is not law, but it is the accepted standard for electrical work in the UK.

Also you don't normally see cables with just brown, black and earth. So that suggests there is a grey wire somewhere. Wires really should be terminated in a suitable enclosure not just cut short or burried in the wall.
 
Wiring regulations, are not law, but can be used in a court of law, but it seems the parts of the building regulations are law, not saying I agree with the requirements of Part F,
Just as with Part P, Part F of the \building Regs (which, as you say, IS 'law) says virtually nothing - namely (in its entirety) ..
F1.—(1) There shall be adequate means of ventilation provided for people in the building.
(2) Fixed systems for mechanical ventilation and any associated controls must be commissioned by testing and adjusting as necessary to secure that the objective referred to in sub-paragraph (1) is met
Anything beyond that (regardless of where it is written) is neither a "requirement" nor "law".

What are the "requirements of Part F" which you say you do not necessarily agree with ?
 
What are the "requirements of Part F" which you say you do not necessarily agree with ?
The requirement for those who fit bathroom extractor fans to take courses, and show they know what they are doing. Yes I can see how easy it is to get it wrong, I sat back and looked at why old house had a problem, and mothers house and this one does not, and realised it was the gap under the shower door in old house, causing a chimney effect so moisture spread through the whole room. This has nothing to do with fitting of the fan, it is all to do with the showering in the bath, where impossible to have a door seal at the bottom.

The fan installer can attend as many courses and join as many schemes as he likes, it will not help.
 