I am planning to cut and reroute 2 core and earth cables 50mm lower through precut holes in noggins. Specifically three x 2.5mm2 cable and one x (either 6mm2 or 10mm2, I can't tell which) cable. The noggins were added to better support the floor above. All three cables should fit through the precut 18mm diameter hole
The problem is that, according to the circuits, each 2.5mm2 could be part of a B32 ring main and the 6mm2 or 10mm2 is part of either a B32 or B40. B32 is 32A and B40 is 40A so larger than the 30A provided by the Essentials junction box.
On the screwfix site it says that the 'Essentials 30A junction box' can do 6mm2 x 2, but it implies 30amps maximum not 32A (B32). Also different sites describe this Essentials box as being 4mm2 x 4 maximum. Website is: https://www.screwfix.com/p/essentials-30a-3-terminal-heavy-duty-junction-box-black/7552d
Or I could massively over do it and use 100A x 4 (one for each 2.5mm2 and one for the 6mm2 or the 10mm2 cable), screwfix website link:
https://www.screwfix.com/p/british-general-100a-heavy-duty-junction-box-97-x-42-x-55mm-brown/661xg
Pics below:
Any suggestions of what junction boxes I should use for the 2.5mm2? I don't know what junction box to use. Can a '30A junction box' be used with a 2.5mm2 32A (B32) ring main?
Maybe I should be extra careful and use 100A for each that way I can't go wrong!
The problem is that, according to the circuits, each 2.5mm2 could be part of a B32 ring main and the 6mm2 or 10mm2 is part of either a B32 or B40. B32 is 32A and B40 is 40A so larger than the 30A provided by the Essentials junction box.
On the screwfix site it says that the 'Essentials 30A junction box' can do 6mm2 x 2, but it implies 30amps maximum not 32A (B32). Also different sites describe this Essentials box as being 4mm2 x 4 maximum. Website is: https://www.screwfix.com/p/essentials-30a-3-terminal-heavy-duty-junction-box-black/7552d
Or I could massively over do it and use 100A x 4 (one for each 2.5mm2 and one for the 6mm2 or the 10mm2 cable), screwfix website link:
https://www.screwfix.com/p/british-general-100a-heavy-duty-junction-box-97-x-42-x-55mm-brown/661xg
Pics below:
Any suggestions of what junction boxes I should use for the 2.5mm2? I don't know what junction box to use. Can a '30A junction box' be used with a 2.5mm2 32A (B32) ring main?
Maybe I should be extra careful and use 100A for each that way I can't go wrong!