- Joined
- 4 Oct 2005
- Messages
- 555
- Reaction score
- 0
- Country
The last few weeks have opened my eyes to the ineptitude and lack of enthusiasm for catching the cowboys at CORGI and the HSE; to elaborate...
Called to new customer's house to investigate lack of heating or hot water function from new boiler installation (regular system boiler 24kW). Installer had scarpered after being paid. Found very poor installation standards including:-
1. Poor soldered joints, two weeping, one compression joint where the 22mm pipe just pulled out (=stained ceiling).
2. It's a system boiler, but the installer had reused the old pump external to the boiler.
3. Installer had re-used old F&E tank, proving to me that he didn't have a clue about system boilers.
4. Condensate drained directly into a bucket.
5. No safety relief pipework installed (and system boiler has isolation valves so F&E could be made ineffective)
6. Three port valve mounted so that head could not be removed without removing the whole valve first, installer had chiselled away at the plaster/wall in a previous attempt to solve lack of heat problem.
7. Here's the best one, heating flow pipework from the 3-port (port A) was connected to a 22mm pipe which ran 2 feet under the floor before terminating in a stop-end. NO HEATING, I WONDER WHY?!!!!
Now to the gas defects:-
8. Undersized pipework, 7m of 15mm copper pipe + 9 elbows; inlet pressure at boiler dropped to 14mB at "full" rate, 20mB at the meter.
9. Gas leak, tightness test revealed a 4mB drop over 30 seconds! Poorly soldered joint to blame, plus loose compression nut at boiler. Remember, this boiler had been left "in working order" and with gas connected.
10. Badly supported pipework, 15mm horizontal run of 2.2m without a clip in sight.
11. Vertical flue terminating within 200mm of chimney breast, BS5440 and MI say min 1000mm.
And finally:-
12. Open electrical junction boxes.
13. 13A fuse on heating circuit.
14. Wiring error causing short when roomstat set low (destroyed programmer, see also 13 above!)
I think you'll agree a very poor and unsafe job.
So what did I do about it? Before correcting I took copious quantities of photos, and invited the customer's friends and neighbours over to see the evidence.
Because of the gas leak caused by poor workmanship I reported it to the HSE under RIDDOR regs, and tried to get the Building Inspector and CORGI involved.
CORGI told me to get the customer to complain to them: she did.
They sent her a form: she filled it in & returned it.
The Building Inspector didn't want to know about the non-conformance to Doc L1 or Doc P "as the installer self-certified the installation".
The bozo Richard-head waste of space installer was, and still is, CORGI registered.
All this took place in early January 2007. To date (end March 2007) neither CORGI nor HSE nor Building Inspectorate have visited the house. She has had no proper heating during this period. and no cooking until I got fed up waiting and corrected the leaks and upgraded the gas pipework. The boiler is still off but now she can cook.
If ever there was a case for a cast iron prosecution this must have been it, but because of the authorities lack of action I have been forced to correct most of the faults, so now the case is weaker.
Glad to have got that off my chest, thanks for reading.....
And finally:-