Sorry I changed my mind and edited.
Curb your imagination. It was like that when the landlord bought the house, one week before we moved in, therefore it points to the previous owner.
I'll have a go at it over the weekend and see if I can either get the full panel down without too much damage to the surrounding area or make the aperture larger and fit new doors.
I have a suspicion that despite the cable sizes there should still only be one spur off the house socket. Is that correct?
Have we not been told that it is 3 x 10mm² singles, which is rather different from "one 2.5mm² cable" (and, presumably, more than adequate)?No, but if there is only one 2.5mm² cable going to the two SWA cables then it is one spur with too much connected to it.
Have we not been told that it is 3 x 10mm² singles, which is rather different from "one 2.5mm² cable" (and, presumably, more than adequate)?
Kind Regards, John
Ah, yes, sorry, my mistake.
I initially replied with just a "No" and then thought I had better qualify that and must have got confused.
The idea is three wires can grip OK in a single terminal but four wires can leave one not gripped, so with some units you can take two spurs as the device has multi terminals, or it is a radial not ring, with the ring consideration must be given to overload if close to the consumer unit, in centre of ring the MCB will protect but close to CU to stop overloading one leg the norm is to connect direct to the MCB so that has three wires in it.Not correct. Two spurs can come from the same point.