Does anyone here have any experience with these?
I was called to an RCD fault yesterday on a split load set up.
It was a 30mA RCD feeding all the sockets, shower, imm heater and central heating.
I ramp tested the RCD in isolation and it tripped at 22.5mA, then re-tested with the installation connected and it tripped at 1-2mA.
I then tested each circuit individually. A couple of circuits tripped the RCD at for example 19mA = 3.5mA for that circuit and the total leakages added together was 13mA. This shouldn't cause any problems for the RCD.
My first thought was a N-E fault with the additional load of the other circuits driving more current through the fault, so I broke down the installation and IR tested L&N>E of each circuit. The lowest two readings were 6.5MΩ and 68MΩ. The rest of the circuits were all ≥100MΩ so whilst not ideal, nothing that should really cause any concern.
I then tried to connect my multimeter between the earthing bar and the main earth with it set to AC mA range, but I have reason to doubt the readings were accurate as they did not tally with what my calibrated MFT was saying on the ramp tests.
I don't know if this was just due to a crappy multimeter or an incorrect method of testing.
Now to my question. I've seen my wholesalers sell a mA clamp meter. How do these work, and would they be any use for tracking this sort of fault?
Do they give a highly accurate reading when clamped to the line meter tail or do they just give a mA reading when clamped to the main earth conductor?
My immediate thought with this is that if it only reads the mA current in the main earthing conductor that it would be of no use for tracking leakage faults if the earth leakage is to true earth such damp penetrating an external or underground joint.
Sorry for the long post, but I though it would be more helpful to give you the thinking behind looking to purchase one of these testers.
I was called to an RCD fault yesterday on a split load set up.
It was a 30mA RCD feeding all the sockets, shower, imm heater and central heating.
I ramp tested the RCD in isolation and it tripped at 22.5mA, then re-tested with the installation connected and it tripped at 1-2mA.
I then tested each circuit individually. A couple of circuits tripped the RCD at for example 19mA = 3.5mA for that circuit and the total leakages added together was 13mA. This shouldn't cause any problems for the RCD.
My first thought was a N-E fault with the additional load of the other circuits driving more current through the fault, so I broke down the installation and IR tested L&N>E of each circuit. The lowest two readings were 6.5MΩ and 68MΩ. The rest of the circuits were all ≥100MΩ so whilst not ideal, nothing that should really cause any concern.
I then tried to connect my multimeter between the earthing bar and the main earth with it set to AC mA range, but I have reason to doubt the readings were accurate as they did not tally with what my calibrated MFT was saying on the ramp tests.
I don't know if this was just due to a crappy multimeter or an incorrect method of testing.
Now to my question. I've seen my wholesalers sell a mA clamp meter. How do these work, and would they be any use for tracking this sort of fault?
Do they give a highly accurate reading when clamped to the line meter tail or do they just give a mA reading when clamped to the main earth conductor?
My immediate thought with this is that if it only reads the mA current in the main earthing conductor that it would be of no use for tracking leakage faults if the earth leakage is to true earth such damp penetrating an external or underground joint.
Sorry for the long post, but I though it would be more helpful to give you the thinking behind looking to purchase one of these testers.