Is there still the potential that there is some kind of damage on the supply side which could be causing this?
Only excess voltage. You would need a recording voltmeter, or a peak recorder to detect that, but I would expect appliance damage.

Is there still the potential that there is some kind of damage on the supply side which could be causing this?
The fact it's different fuses supplying different installations rules out problems with the cable(s) to the various different parts - if one of those was damaged, then it would be the same fuse every time.in the past it was two different fuses.
The only common item to all of the installations and the four fuses is the incoming cable itself - and the only plausible failure there is that the neutral is loose/failing, so installation current is returning via that nasty looking earth connection on the outer sheath.Is there still the potential that there is some kind of damage on the supply side which could be causing this?

OP - what is your interest in this?


That is quite a reasonable questionI have just skimmed this, but could phase imbalance come into it at all?

exactly... why do we bond external pipe work or in this case are there two main earthing arraignments, one with a spark inducing voltage and one without.Could there a PD between the two?
The only way that would be an issue is if the neutral were lost, in which case both supplies would effectively be in series across 2 phases. The chances of a flat and a shop being balanced is extremely low, in which case one of them would be receiving substantially more than 230V.I have just skimmed this, but could phase imbalance come into it at all?