What is the maximum size appliance you can run from a switched fused spur on a ring?? I had 2200W in my head, is this correct? Cheers
 
if it's a fused spur it can have max 13A fuse in it

About 3kW
 
I dont think that is correct... not if its a fixed applicance... anyone else able to enlighten us..... :?
 
You can safely run 13A / 3kW from an FCU supplied by a ring.

However, it is not good circuit design, and large fixed loads should really be fed from their own dedicated radial circuit.
 
I dont think that is correct...

So why you f'in asking, then? If you think the answer you're gonna get is wrong, what's the point in asking? :roll: :roll:

As RF says, it's not good design, however, rings often support loads of 13A.

Whether they're fixed or not I'm not sure makes much difference: it's still a 13A load.

You have 2200W in your head: why? And what difference does the extra 800W or so make?
 