could anybody tell me if type1 mcb is the same as type A .our mcb keeps cutting off for no reason. i read on the forum that if i changed from type A to type B it might help. I bought one from ebay a Mem 32a 321qeb type B our old one was a Mem 32a 321qeb type 1 and it was worse than ever couldnt even get the electricity to stay on . i dont understand it.
its the same mcb that keeps blowing at various times for no reason.Can anybody help i don,t know if we need a full new fuse box
 
Sponsored Links
patricia.burns2 said:
for no reason

this is almost certainly not true.

What loads are there on the circuit?

What damage is there to the cable and accessories (including rodents and nails)?
 
it is all the down stairs sockets and some garden lights but we have tried unplugging them but it still keeps blowing. its alright for days sometimes but today its blown about three times and just blows again without touching anything
 
JohnD said:
patricia.burns2 said:
for no reason

this is almost certainly not true.

What loads are there on the circuit?

What damage is there to the cable and accessories (including rodents and nails)

it is all the down stairs sockets and some garden lights but we have tried unplugging them but it still keeps blowing. its alright for days sometimes but today its blown about three times and just blows again without touching anything?
 
Sponsored Links
has it been raining today?

If you are SURE that there was nothing plugged into the circuit when it tripped (no cooker, no immersion heater, no fridge or freezer, no kettle) and you are SURE there are no damaged sockets or switches, and you are SURE there is no water in contact with an electrical part, and you are SURE there are no loose connections in any of the accesssories or spurs, then you probably have damaged cables.

Common causes are a nail through a wall or floor, or mice gnawing cables under the floor. a competent electrician should be able to trace the damaged section and replace with new cable.
 
Type A MCBs only exist for VERY specialised applications, if at all. ;)
 