411.3.3 Additional protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket-outlets with a rated current not exceeding 20 A that are for use by ordinary persons and are intended for general use, and
(ii) mobile equipment with a current rating not exceeding 32 A for use outdoors.
An exception to (i) is permitted for:
(a) socket-outlets for use under the supervision of skilled or instructed persons, e.g. in some commercial or industrial locations, or
(b) a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
This is general for all items but:-
709.531.2 RCDs
Socket Outlets shall be protected individually by an RCD having the characteristics specified in Regulation 415.1.1. Devices selected shall disconnect all poles. including the neutral.
Final circuits intended for fixed connection for the supply to houseboats shall be protected individually by an RCD having the characteristics specified in Regulation 415.1.1. The device selected shall disconnect all poles, including the neutral.
Is for MARINAS AND SIMILAR LOCATIONS I would assume the guy in NIC who said as long as the commando skt is clearly labelled as for
Specific use ONLY then its fine???? did not know it was for a Marina.
There are special RCD's that auto reset and also special rules where loss of supply could cause danger, but the reams of paperwork required and HSE involvement mean it really is last resort. With a batching plant I worked on we had monitors rather than trips because of the drastic results from power loss but it required the unit to be always manned and "The RCCBs have only tripped few times in 4 months." does not really warrant that sort of approach.