OIL - Atkinson Tankmaster blocked

Joined
6 Dec 2025
Messages
2
Reaction score
0
Country
United Kingdom
Afternoon All,

New here so be kind!

We’ve got an Oil boiler for our central heating and hot water and ran out of oil 4 days ago (I know, I know, already had it in the ear from the missus who is currently in labour!).

The long and short of it is that having topped the tank up and attempted to bleed the burner pump, no oil or air was coming through.

Undone the fitting before the fire valve outside, and there is no oil in the line.

Having inspected the tank, I have seen we have a very old and battered Atkinson Tankmaster fitted. The filter has probably never been changed, as with everything in this house it seems bodged and reused within an inch of it’s life.

I’ve pretty heavily researched the valve and think I’ve got my head around how it works. I wanted to check the filter on it and the pipework around it to try and establish if any oil was coming through the valve or if the block is between the Atkinson valve and the fire valve.

On further inspection and attempts to turn the hand wheel. It spins freely in both directions and doesn’t seem to pull the spindle in or out. When I press the spindle it moves in about half a centimetre indicating that the plunger is shut.

Obviously we didn’t have this problem before (that I’m aware of) as our oil was flowing freely.

Any ideas for the best way to rectify it or next steps. Should have the plumber coming back at some point but with an imminent newborn on top of Christmas this could be tricky.

TL;DR: Atkinson Tankmaster wheel spinning freely, spindle is out all the way and oil line is blocked somewhere.

Thanks again! C
 
Last edited:
If you’re sure the valve is shut, you can take off the bowl on the bottom & check the filter. You might get away with giving it a quick scrub over with an old toothbrush to get you going temporarily.
 
If the wheel spins freely, then the thermal joint has broken. The nut should still be on the spindle, and can be turned with a spanner to close the valve. The valve is closed when there is no play in the spindle. You can then remove the filter bowl.
 
Is the tank outlet higher or lower than the inlet to the pump.
I would imagine it’s ever so slightly higher but that would be a complete guess because the run is about 10 metres long.

If the wheel spins freely, then the thermal joint has broken. The nut should still be on the spindle, and can be turned with a spanner to close the valve. The valve is closed when there is no play in the spindle. You can then remove the filter bowl.
Would you be able to tell this from an image? I have attached one to this response.

If you’re sure the valve is shut, you can take off the bowl on the bottom & check the filter. You might get away with giving it a quick scrub over with an old toothbrush to get you going temporarily.
I’m not certain it is. That’s the problem. Didn’t want to take it off if it isn’t actually a bit open.
 

Attachments

  • IMG_6156.jpeg
    IMG_6156.jpeg
    282.5 KB · Views: 10
Last edited:

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top