Old junction boxes in two plate wiring / power sockets

Joined
15 Feb 2008
Messages
253
Reaction score
10
Country
United Kingdom
IMG_6978.jpeg
I’ve quite an old bungalow and I’ve noticed as I’m changing the old and various ceiling light fittings that the roses only have one wire.
The age of the property and absence of a Neutral at switch suggests a ‘two plate’ system.
Similarly, my power sockets (that I’ve changed so far), only have single wires and first I assumed they were spurs.
In the loft I have two large connection/junction boxes - I assume one for the lights and one for the power sockets; I’ve added a picture below.

I’ve no idea if this is ‘normal’ for age of the property; it was likely re-wired in 1950s and I suspect these dusty old boxes haven’t been disturbed in years.
Should I get them inspected and/or change to a modern connector box.

I’ve recently extended the property and had some additional wiring added; cooker, sockets, lights etc.
The work included a new consumer unit and the necessary testing, certification and notification; everything tested okay.

Thanks D
 
Junction boxes in the loft with a single cable at each rose and socket is normal for a lot of 1950s-60s wiring. The lights are wired by the junction box method (feed, switch drop and lamp cable all meet in the box) rather than loop-in at the rose, so the layout itself isn't a fault.

What matters is the condition:

1. If the cables are rubber insulated (VIR or TRS, often a black or grey rubber sheath), the rubber goes brittle with age and can crack when it's moved. Opening and tidying those boxes is exactly when it fails, so check the cable type before touching anything.
2. Screw-terminal junction boxes need to stay accessible for inspection (BS 7671 526.3). In the loft they are.
3. Look for scorching, loose screws and missing earths. 1950s lighting often has no CPC, which matters if you fit metal light fittings.

The new consumer unit will have had some testing, but it's worth asking the electrician whether the old circuits got a full insulation resistance test or just the new work. If not, I'd get an EICR on the old circuits. That test tells you far more than looking at the boxes, and if the old cable turns out to be rubber, that's a rewire conversation rather than a box swap.
 
Those are not 50's with plastic clips, but not much later. Years back having a big junction box for the lights was not uncommon, there were various options in those BICC boxes, chances are there's 3 brass bars for earth, live and neutral and a series of terminals for the switched live between the switch and light cables, 5 IIRC or maybe 6. I haven't seen one for many years.
 
I could be wrong, but I don't think the OP's cables are rubber.

If it were me I'd take the lids off the boxes and take a quick look at the wiring. If it looks in good condition then I'd leave it at that.
 
I could be wrong, but I don't think the OP's cables are rubber.

If it were me I'd take the lids off the boxes and take a quick look at the wiring. If it looks in good condition then I'd leave it at that.
Yeah, looking at the photo again they’re probably PVC, not rubber. In that case just popping the lids off for a look makes sense. Thanks SUNRAY, didn’t know that about the BICC boxes.
 
Thank you for all replies. I don’t have any of that old rubber insulated cable; I suspect the property was fully re-wired in late 50s. That said, I’ve had a look at the recent EIC form and there are values for all circuits in the three columns labelled ‘INSULATION RESISTANCE’. The columns labelled ‘CONTINUITY’ has a few N/A entries but full values in R1 + R2 column. I’m due to get my Electricians back for some other jobs, so I’ll ask that they do a visual inspection on the junction boxes and torque up anything should it be loose.

As an aside; I have been thinking about adding some SHELLY type relays to one or two circuits; would my ‘wired by the junction box method’ better facilitate this with access to neutral and relay in loft space.

Thanks Diggory
 
Show us inside the boxes if you can do it safely....I've never seen them before im intrigued....I think its a great idea, one wire at every point.
 
Thank you for all replies. I don’t have any of that old rubber insulated cable;
No those certainly don't look like rubber
I suspect the property was fully re-wired in late 50s.
I'd say more like mid 60's with white Twin &Earth
...

As an aside; I have been thinking about adding some SHELLY type relays to one or two circuits; would my ‘wired by the junction box method’ better facilitate this with access to neutral and relay in loft space.

Thanks Diggory
Oh yes very much easier but you may have to replace the box for additional terminals
Show us inside the boxes if you can do it safely....I've never seen them before im intrigued....I think its a great idea, one wire at every point.
T'was quite common as the follow-on from conduit & singles



Earlier version in bakelite using metal cable buckles
1795085509852.png

And I suspect the reason they moved from bakelite
1795088843432.png
 
Thanks - that’s interesting.
The oldest part of the house is maybe >200 yrs old - so it could; it was re-wired in 60s.
And interesting you mention ‘conduit and singles’ - all my drops from loft are in heavy steel conduit.
So perhaps the re-wire T&E drops were just fed through existing conduits.
The conduits aren’t that generous size wise (ID) - recently replacing one of the TE drops was a bit of a challenge.

Glad that you think mine aren’t Bakelite - you think they are plastic ?

Thx D
 
No those certainly don't look like rubber

I'd say more like mid 60's with white Twin &Earth

Oh yes very much easier but you may have to replace the box for additional terminals

T'was quite common as the follow-on from conduit & singles



Earlier version in bakelite using metal cable buckles
View attachment 426934
And I suspect the reason they moved from bakeliteView attachment 426938
Thise ones are a bit messy compared to the OPs which seem quite neat.
 
I think Bakelite is the same as ABS, which is still used. A hard, thermosetting plastic that does not melt or burn under heat, but chars and smokes.

I was going to say your first picture shows Adaptable Boxes rather than Junction Boxes, but I don't remember seeing that style.

IME the white PVC and clips are more likely 1970's or later. Older stuff I have seen was grey, and the cores Red and Black. Earth sleeving, if present, was plain dark green, not G/Y, and earths frequently snipped off in lighting circuits.
 