Old junction boxes in two plate wiring / power sockets

Joined
15 Feb 2008
Messages
251
Reaction score
10
Country
United Kingdom
IMG_6978.jpeg
I’ve quite an old bungalow and I’ve noticed as I’m changing the old and various ceiling light fittings that the roses only have one wire.
The age of the property and absence of a Neutral at switch suggests a ‘two plate’ system.
Similarly, my power sockets (that I’ve changed so far), only have single wires and first I assumed they were spurs.
In the loft I have two large connection/junction boxes - I assume one for the lights and one for the power sockets; I’ve added a picture below.

I’ve no idea if this is ‘normal’ for age of the property; it was likely re-wired in 1950s and I suspect these dusty old boxes haven’t been disturbed in years.
Should I get them inspected and/or change to a modern connector box.

I’ve recently extended the property and had some additional wiring added; cooker, sockets, lights etc.
The work included a new consumer unit and the necessary testing, certification and notification; everything tested okay.

Thanks D
 
Junction boxes in the loft with a single cable at each rose and socket is normal for a lot of 1950s-60s wiring. The lights are wired by the junction box method (feed, switch drop and lamp cable all meet in the box) rather than loop-in at the rose, so the layout itself isn't a fault.

What matters is the condition:

1. If the cables are rubber insulated (VIR or TRS, often a black or grey rubber sheath), the rubber goes brittle with age and can crack when it's moved. Opening and tidying those boxes is exactly when it fails, so check the cable type before touching anything.
2. Screw-terminal junction boxes need to stay accessible for inspection (BS 7671 526.3). In the loft they are.
3. Look for scorching, loose screws and missing earths. 1950s lighting often has no CPC, which matters if you fit metal light fittings.

The new consumer unit will have had some testing, but it's worth asking the electrician whether the old circuits got a full insulation resistance test or just the new work. If not, I'd get an EICR on the old circuits. That test tells you far more than looking at the boxes, and if the old cable turns out to be rubber, that's a rewire conversation rather than a box swap.
 
Those are not 50's with plastic clips, but not much later. Years back having a big junction box for the lights was not uncommon, there were various options in those BICC boxes, chances are there's 3 brass bars for earth, live and neutral and a series of terminals for the switched live between the switch and light cables, 5 IIRC or maybe 6. I haven't seen one for many years.
 