Hi, I've searched this forum and can't find the same query.
I would like to install a light and socket in my shed and low voltage LED lights in the garden. Before I laid my patio, I laid in 50m of 4mm 3 core SWA in a loop round the garden for any future projects like this!
At present I have the downstairs ring circuit containing 10 double sockets utilising the TV, stereo, lights and DVD, total Power 1.2KW. This ring has a 32A MCB and is RCD 30mA protected. One of these double sockets in the circuit is fixed on the outside wall. Is it possible to extend this circuit to my outside SWA loop. If possible do I need to install a further outside weather proof 30mA RCD.
Hope all this makes sense!
Thanks.
I would like to install a light and socket in my shed and low voltage LED lights in the garden. Before I laid my patio, I laid in 50m of 4mm 3 core SWA in a loop round the garden for any future projects like this!
At present I have the downstairs ring circuit containing 10 double sockets utilising the TV, stereo, lights and DVD, total Power 1.2KW. This ring has a 32A MCB and is RCD 30mA protected. One of these double sockets in the circuit is fixed on the outside wall. Is it possible to extend this circuit to my outside SWA loop. If possible do I need to install a further outside weather proof 30mA RCD.