Dear All,
I’m doing a rear extension and, as part of this project, I have asked an electrician to give me a quote for the electric work.
I suspect he might be trying to sell things are not really necessary by quoting the new Amendment 3 to the Wiring Regulations. Specifically, he says:
1) The existing plastic consumer unit needs to be replaced for a metal one. I’ve checked and my understanding is that this requirement comes into force from 1 Jan 16 and only if you replace the unit. BTW, the existing unit is relatively new, and has got automatic circuit breakers, hearth connection, RCDs and the appropriate equipotential bonding. In a word, is fully compliant with regulations current at the time of installation;
2) All the existing wiring in the existing kitchen, together with the new wiring, needs to be run though metal ducts. Specifically, he is proposing to rewire the existing kitchen and not only to extend the existing ring / lighting circuits. I’ve checked on line and it seems to me that the ducting is not required if PVC cables are buried in plaster cover of 50mm or more, as it is normally the case.
Can you please tell me if this guy is giving me good advice or just taking the mickey?
Many thanks for your help,
Max
That is true. It is not mandatory at the moment.
All sounds fine, then.
Not so.
Did he perhaps say 'conduit'? Still not so, but more explainable.
You most probably could not go that deep because of building regulations but if they are covered by an RCD then you don't have to.
Mmm. It would appear that something is not right.
Many manufacturers are stating that their plastic CUs meet the 'non-combustible' requirement, presumably because they meet the flammability tests of the product standard..
Fair enough and glad to hear it - but as no one knows what 'non-combustible' actually means it will be impossible for us to judge so...
The big problem with the wording of Amendment 3 is that it says that (as of 1st Jan) CUs/DBs etc. must comply with BS EN 61439-3 AND have their enclosure manufactured from non-combustible material. Many people interpret that added "and" clause as implying that BS7671 will be requiring something (not defined) beyond what it required by the Standard - since if they were merely asking for compliance with the 'non-combustibility' requirements of that Standard, that clause would be redundant and stupid.
Kind Regards, John
John, we've had this discussion already. I believe that JPEL/64 has no business writing product requirements into the installation standard, but if they were pressured into doing so, they should have referred to existing flammability standards.
I believe the term 'non-combustible' does have a defined meaning in building material standards, and I have someone looking into that possibility.
Yes, I realise that, but it doesn't really answer my question (not that anyone but 'them' could actually answer it!) ... given that, for whatever reason, they were doing something that they probably shouldn't have been doing, I wonder whether (as their chosen wording seems to imply) they thought they were requiring a degree of 'non-combustibility' beyond what is required by BS EN 61439-3, or what?
Thanks. That will be interesting to know, but I don't think it really lets them off the hook. If they were thinking/relying on some Standard's definition of 'non-combustible', they surely should have referred to that Standard?
Kind Regards, John