Removed spur plug socket - remaining sockets now tripping

Discussion in 'Electrics UK' started by Uni, 23 Nov 2020.

  1. Uni

    Uni

    Joined:
    23 Nov 2020
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Totally puzzled and wondering if anyone could give me some advice how best to proceed please.

    Unused plug socket, so we decided to disconnect and blank out. Opened the socket and found a single cable (which suggests its a Spur?). I terminated individually Neutral / Live / Earth into 30 amp connector block.

    All sockets in the living room now now tripping out intermittently, even without anything turned on. If I turn the electric heater on which used to work fine, everything trips out immediately. If I reset RCD without anything used, after approx 30mins it trips.

    I'm comfortable managing cables safely at sockets and the CU but nothing more, I was hoping to fix myself but I just don't know where to start.

    Any help or advice welcome.
     
  2. Sponsored Links
  3. chivers67

    chivers67

    Joined:
    18 Nov 2008
    Messages:
    1,286
    Thanks Received:
    149
    Location:
    Surrey
    Country:
    United Kingdom
    The Circuit is a Spur or Radial but disconnection it in the way you have shouldn't create any issues unless the Earth & Neutral are somehow coming into contact with one another and tripping an RCD.

    Take the cover off and make sure there's nothing untoward in the first instance.
     
  4. Uni

    Uni

    Joined:
    23 Nov 2020
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Will do, thank you
     
  5. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    35,476
    Thanks Received:
    1,150
    Country:
    United Kingdom
    The other thing you could do is to return the installation to its former state, by refitting the socket you removed.

    If the RCD still trips, it is unlikely that the two issues are related.
     
    • Like Like x 2
  6. endecotp

    endecotp

    Joined:
    2 Dec 2013
    Messages:
    3,908
    Thanks Received:
    501
    Country:
    United Kingdom
    Is the terminal block a dirty old one you found in the back of your garage?

    I guess that previously the earth was connected to the socket back box (if metal) but now isn’t.
    I can’t think how that would cause earth leakage to increase, but it is a difference from how it was before.
     
  7. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    67,825
    Thanks Received:
    3,712
    Location:
    Coastal
    Country:
    Cook Islands
    you may have got a whisker of wire touching the backbox, or something crushed or pierced by a screw.

    is the old insulation black and red PVC? not rubber, or lead, or cotton, or sticky tape?

    is there any sign of damp?

    your fault may be difficult to trace, but it leans towards neutral to earth leakage.
     
    Last edited: 23 Nov 2020
  8. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    35,476
    Thanks Received:
    1,150
    Country:
    United Kingdom
    How goes it, OP?
     