Even with all circuits RCD protected, you still can not ensure compliance with some the regs BAS listed.
With a CU swap you probably would fit RCDs as a matter of course - the extra cost is pretty insignificant, and it's sensible future-proofing. What we're really talking about here is the idea that you can't replace 3036s with plug-in MCBs because doing that means you have to add RCD protection.I can imagine a few angry faces if one week I replaced a consumer unit, then the following week they wanted something added which I say I cannot do without RCD protecting the circuit at the consumer unit![]()
And lots I didn't list...Even with all circuits RCD protected, you still can not ensure compliance with some the regs BAS listed.
That was silly nitpicking, 30mA RCD protection is the only option to protect an older installation without, unless you want to rip the place apart!Even with all circuits RCD protected, you still can not ensure compliance with some the regs BAS listed.
The original argument revolved around the installation of an RCD to comply with the 17th, if MCB's were used to replace Fuses.No it isn't silly nit-picking.
RCD protecting an installation would not suddenly make an inaccessible screwed joint (as mentioned in the example BAS gave above) compliant with the current edition of BS7671, so you would still have a non compliant installation.
As you pointed out, the only way to ensure an installation is fully compliant is to rewire it your self.
Why single out the requirements of regulation 522.6.7 and insist that the installation complies with this, yet ingnore (as in the example above) the requirements of 526.3?
The argument revolves around your insistence that an RCD must be installed so that the installation complies with one of the requirements of the 17th.The original argument revolved around the installation of an RCD to comply with the 17th, if MCB's were used to replace Fuses.
Indeed not, so acting on the basis that you cannot do Job X without also doing Job Y because other parts of the installation which were and are nothing to do with you, and which you are not touching, require Job Y to conform to just one particular requirement of the 17th is at best illogical.There is no magic wand that will raise the installation to the requirements of the 17th.
So FOR THE FOURTH TIME OF ASKING, why do you insist that additional work must be done in order to bring the rest of the installation into compliance with 522.6.7 but not a single other one of the many regulations with an equal status in BS 7671:2008? What is it that you feel you cannot do unless you make what's already there comply with 522.6.7 but you can do without making what's already there comply with 522.6.5, 522.6.8, 522.6.5, 521.10.1, 526.3, 522.8.10 etc etc etc?A PIR is recommended by both NAPIT and the NICEIC prior to carrying out a DB change, this is required to detect existing faults. Replacing fuses with MCB's would require an EIC to be completed, I would treat this as a 17th DB change, requiring separate RCD protection for lighting and power - although poor engineering and more expensive.
Which it is, why would you think not, for an alteration to a fuseboard post 17th introduction?The argument revolves around your insistence that an RCD must be installed so that the installation complies with one of the requirements of the 17th.
This is the most important change to the 17th RCD - the requirement for whole house protection and a must!Indeed not, so acting on the basis that you cannot do Job X without also doing Job Y because other parts of the installation which were and are nothing to do with you, and which you are not touching, require Job Y to conform to just one particular requirement of the 17th is at best illogical.
And why?
Re the fuse/MCB debate...
If the RF is wired in 2.5/1.0, does a 3036 comply with regard to disconnection times?
This is the most important change to the 17th RCD - the requirement for whole house protection and a must!![]()
Did I say every circuit? Of course there are some exemptions - with provisos. I'll leave it to you to spell them out.Since when was it a must for RCD protection on every circuit?This is the most important change to the 17th RCD - the requirement for whole house protection and a must!![]()