10.5+27.0=37.7 Max demand
37.7*30%=11.25 Amps
11.25+10=21.25
Total with diversity = 21.25 Amps
Nah - I'm not the one pursuing a pathetic and childish personal vendetta from topic to topic, repeatedly accusing someone (without ever being able to justify it of course) of being a bully, or mentally ill, etc.
Is that over a range of 220-240V, or 230-240?I’ve looked up the manual of the built in oven I was thinking off (max draw 2250w-2400w
At what voltage?I’ve looked up the hobs usage and with all of them on its 6200w
Cooker diversity is 10 Amps plus 30 % of the total demand, I used to use BAS formulae but it is very clear in the OSG Page 97 that it is10A+30% of full load.
As BAS states it is a significant difference, hence I was pulled up on this, easy mistake as it is the typical wording of the OSG
And equally clear on page 96 that it's 10A + 30% of the remainder.Cooker diversity is 10 Amps plus 30 % of the total demand, I used to use BAS formulae but it is very clear in the OSG Page 97 that it is10A+30% of full load.
But you're right - OSG Table 1B says something different to Table 1A, just as it did in the 16th one. I'd never noticed, nor have I ever seen it mentioned anywhere.As BAS states it is a significant difference, hence I was pulled up on this, easy mistake as it is the typical wording of the OSG
Is it in there?I am not a whizz on the pc so cannot provide a link to the 7671
That wholesaler is actually hosting a copy of a respected guide to the Wiring Regulations.which is what I tend to use rather than an electrical wholesalers page!
I said you got it wrong, not that you were incompetent.I do wonder about the coments previously made about my incompetence,
As well as the OSG, and Paul Cook's books, you'll find the same 10A + 30% of the remainder in GN1, Whitfield, the Amicus guide to the regulations, NICEIC's Domestic Electrical Installation Guide.....how many cooker circuits have you wrongly installed
Uncalled for.Mr armchair sparky?
It's not a fact, it's a fantasy of yours for which you can provide no rational justification whatsoever. And now I see you've decided to say I'm mentally ill. Are you a qualified psychiatrist?1. I don't pursue you, when another comments I just draw to their attention the facts about you.
Oh - I see - because I don't accept the truth of your allegations they must be true. That makes sense.2. I have tried to explain to you why you are a bully, (once) but like most bullies, you choose not to accept that you are one.
Falsehood.3. You have been banned from another/other forums for the same thing. Fact.
Sorry Matt, easily distracted!
I personally wouldnt do it, it will cause significant load on one side of the ring and with that amount plus a kettle, toaster and microwave could cause problems.
Sorry mate looks like back to square 1!